Discuss Load and heat in the UK Electrical Forum area at ElectriciansForums.net

G

Gordon lees

Hello. New to this forum stuff so hopefully this makes sense. I've recently installed a 10mm 3core cable (H07FN-R) to power a 12kw electric boiler. On full power the boiler is drawing 46Amps. I'm a bit concerned as the cable is omitting a slight heat when drawing this load, was just wondering if this is normal?
 
It's a considerable load. If no heat was generated then there would be no need to use such a big cable! Daz
 
the cable will normally get a bit warm. most cable is rated up to 70deg.C. a slight warming is usual, considering the ccc of the cable. problems may arise if cable is covered in insulation. this reduces the ccc by up to 50%.
 
Hello. New to this forum stuff so hopefully this makes sense. I've recently installed a 10mm 3core cable (H07FN-R) to power a 12kw electric boiler. On full power the boiler is drawing 46Amps. I'm a bit concerned as the cable is omitting a slight heat when drawing this load, was just wondering if this is normal?
Bit more info required:
How is the cable installed
How long is the run
Voltage
type of supply The list goes on
 
slight heat is warm, as opposed to much heat which is hot. not to be confused with the current sun's heat which is bloody cold at present. :eek:
 
Bit more info required:
How is the cable installed
How long is the run
Voltage
type of supply The list goes on


The cable is installed in void above a small cupboard space housing the water tank and this new boiler, as well as the electricity meter etc.
Cable run 6m max
230V. Protective device 63A 30mA RCD.
 
Bit more info required:
How is the cable installed
How long is the run
Voltage
type of supply The list goes on
The cable itself has 3 layers of insulation, quite thick as well. Conductors single insulation and two outer layers, obviously to withstand high external temperatures.
 
The cable itself has 3 layers of insulation, quite thick as well. Conductors single insulation and two outer layers, obviously to withstand high external temperatures.
I googled this cable and max temp is 60deg
 
Intrigued to see the answer to Andy's question about over current protection . Daz
 
Intrigued to see the answer to Andy's question about over current protection . Daz
Well it's been a learning curve finding out the RCD isn't offering over current protection. Will need to replace with an RCBO as soon as possible. Can't seem to find one rated at 63A though. Jesus....
 

Reply to Load and heat in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
15
Views
553
Hello All I was hoping for some advice. We have a microwave and recently after cleaning, as soon as the microwave was plugged in, a loud humming...
Replies
3
Views
747
  • Article
Do you install new heating systems? Ever had a missing cable run between a boiler and a pump? Using MAINSLINK - the pump overrun solution - you...
Replies
0
Views
692
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock