Discuss Load concern in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
0
Hi All and thanks to those who take the time to reply.

My concern is the amount of current the building could pull in use. I will try and give some salient facts.

160 flats over 8 floors. The landlords areas per floor consist of 20 x 20W led lights and several occasional cleaners sockets hence a few amps per floor - I'm not worried about these.

Other noteable loads are...

The laundry has 10 x 25A washer / driers.
The lift is 3 phase and is rated t 30A
The water is pumped to all floor and the pump can draw 60A.

Each flat (160 of them) has seven circuits. Hob (4KW) - 20A breaker. Heater (1KW) - 6A breaker . Ring-32A breaker . Lighting 6A breaker. Fridge-6A breaker. Shower (7.5KW)-32A breaker. Water heater (3KW) - 16A breaker.

The incoming supply is a 400A 3 phase PME, so 1200A total.

As the flats are "all bills included" the occupants will think nothing of leaving the heats on all the time and a 1K heater never thermostatically switched off as the rooms are so big. So 160 a 4A (1KW loading) = 640A. That's half the supply taken already and would only leave 3.5A per flat.

When I have raised my concerns I have been told not to worry but I do.

With diversity you're looking around 60A (someone may correct me on the exact figure). 60A x 160 flats = 9600A. That's a bit over a difference from the incoming 1200A.

Perhaps there are special calculations as all flats may not be in use at the same time etc. But with the info I have given can person(s) put at mind at rest and confirm the 1200A supply is more than capable?

Once again, cheers for reading and for any reples.
 
A clamp ammeter or 3 might resolve some of the concerns.

I'm sure that the National Grid managers fear the day everyone leaves at least 1 light switched on.
 

Reply to Load concern in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
803
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
984
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock