Discuss Loss of supply alarm in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Reaction score
362
Customer feeds an outhouse via a RCD fused spur. Tripped a couple of times in the last 6 months and because there is a freezer out there potential to not know supply has tripped and lose all thats in the freezer.

Anybody had cause to use some sort of alarm in the event of the RCD tripping.

Was thinking about using an emergency light, but that'll only work for 3 hours and relies on somebody going into the room where the supply is. Could rig up something with a relay and a buzzer, but why re-invent the wheel when somebody has done it already.

Ideas gratefully received!
 
Security or fire alarm psu with battery backup......simply relay & buzzer, if power fails buzzer sounds. A simple 1 amp psu with 7 a/h battery will give a 30mA sounder over 200 hours of operation
 
Security or fire alarm psu with battery backup......simply relay & buzzer, if power fails buzzer sounds. A simple 1 amp psu with 7 a/h battery will give a 30mA sounder over 200 hours of operation

Thanks, but was thinking don't really need a battery (which is relatively large) as I have a permanent supply supplying the RCD spur!

My thinking was to have the RCD'd supply energising a relay, if supply lost, relay changes over and permenant supply powers a sounder!
 
Same principle, but a cheap psu gives you the lower voltage for sounder and the benefit of sounding if all power is lost
 
If the installation had an intruder alarm with a spare zone , you could install a relay ,normally energised from the load side of the RCD fused spur and allocate the alarm input to a 24 hr zone.
 
I've seen baby mains powered monitoring units sound off when the transmitter loses supply, the receiver makes a loud 'white noise' sort of sound, maybe that setup could work temporarily until a more professional solution be found.
 
Have a search for main power failure alarm plugs a lot of the systems will provide texts to phones, some of them provide local alarms, generally cost over £100 this basic one is £68 or they are available with EU plugs from china for about £20, save any messing about wiring stuff up, who would want to do that!!
 
If the supply is using SWA cable and the cabling in the shed is surface, I would remove the plug from the freezer and wire it using a FCU. If they need another socket in the shed then fit an RCD socket
 
If the supply is using SWA cable and the cabling in the shed is surface, I would remove the plug from the freezer and wire it using a FCU. If they need another socket in the shed then fit an RCD socket
or label the socket outlet as dedicated to freezer.
 
I wouldn't hardwire it to an fcu. Makes it expensive when the fridge fails and they need to get a sparky in to disconnect it and reconnect the new one. Daz
 
You could use an RCD with an auxiliary contact which operates an alarm when tripped

Or if the freezer has an auto defrost function check the heater element is not on it's way out seen this cause problems many times in the past
 
I wouldn't hardwire it to an fcu. Makes it expensive when the fridge fails and they need to get a sparky in to disconnect it and reconnect the new one. Daz

Really? How often does a fridge/freezer fail? Sounds like they have lost a couple of full freezer loads full already!
 
At some point the fridge will need replacing. Then they will need to get a sparky in to disconnect/re-connect. Better on a plug top. Daz
 
It's easy, you just stick a relay like this: Schrack PT270T30 230V Relay With LED FD5C9 | eBay after the RCD, connect the normally open when energised side to this: https://www.tlc-direct.co.uk/Produc...owC6NhCe55twXc74aBtg-C9J3If9cm8JnyBoCd8rw_wcB , and feed mains to the input of that relay from before the RCD. RCD trips, contacts close, mains from before the RCD directed to the alarm. They will sharp know about it!!

Ok, maybe the bell is overkill, but you get my point. It's cheap and easy to do. :)
 

Reply to Loss of supply alarm in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
544
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
TLDR: is there a legal requirement to have a landlords supply to power an L2 alarm system? Mornin'. Non-electrician, under the cosh from an iffy...
Replies
6
Views
2K
Hi all, Was called to a job today with intermittent RCD tripping from the garage. Standard domestic TNS with three core SWA from the house to an...
Replies
7
Views
986

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock