padawan

Hey guys :)

I need to terminate 6mm T&E, plus 6mm earth single, and 6mm SWA into an IP65 junction box.

The junction box i am using is this one

https://www.tlc-direct.co.uk/Products/LB9065.html

The SWA will be glanced into the 20mm knockouts, and the 6MM T&E and 6mm earth single will be rear entry, so far so good. I then noticed that the rear entry knockouts are both M16, which is a new one on me. I have had a look online but i can't find any M16 grommets (TLC don't stock them), the only thing i can find is m16 glands but obviously thats no good due to rear entry into the junction box.

Im not sure what i am missing, can someone please point me in the right direction.

Thanks

P.S. Please excuse my ignorance.
 
i'd not b other. just seal around the box to the wall after fitting. making sure there's a 4-5mm drain hole in bottom of box
 
Cut a 20mm grommet down to fit snugly, works fine if cake is not going to be disturbed.

And even cable too!
 
Last edited:
Don't know about you but I would use blind grommets to try and overcome the IP issue, but then thats just me.

Blind grommets won't be any good for maintaining the IP rating of the box.
The box is IP 65 so to maintain that you would need an IP 65 stuffing gland with suitably shaped insert to seal on the T&E
 
Blind grommets won't be any good for maintaining the IP rating of the box.
The box is IP 65 so to maintain that you would need an IP 65 stuffing gland with suitably shaped insert to seal on the T&E

You are right I thought that as I pressed the reply button, must be the red wine again I tend to blame that a lot but it is true the Cotes Du Rhone does tend to dull the sensed especially after a bottle
 
Thanks for your replies guys, seems it was a stupid question :oops:

The box is plastic so why do you need a grommet?

I suppose it doesn't as there is little risk of snagging the cable, normally when i have come across knockouts it been a case of glands or grommets, but i guess sometimes it hard to see the wood for the trees lol.

i'd not b other. just seal around the box to the wall after fitting. making sure there's a 4-5mm drain hole in bottom of box

Cheers that sounds just the ticket.

Cut a 20mm grommet down to fit snugly, works fine if cake is not going to be disturbed.

And even cable too!

Im not sure why i didnt think of this lol, but great tip thanks.

And after successfully installing, eat the cake. Jobs a goodun.

Cake is always welcome :p
 
The junction box i am using is this one

https://www.tlc-direct.co.uk/Products/LB9065.html

The SWA will be glanced into the 20mm knockouts, and the 6MM T&E and 6mm earth single will be rear entry, so far so good. I then noticed that the rear entry knockouts are both M16...

What makes you think that there are two 16mm knockouts in the back of the box? I can't see them in the photo on the TLC page you've linked to.
 

Reply to M16 grommets in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
595
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
772
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
487

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock