Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
You are supposed to verify the continuity of the conductor when disconnected so it is all about the csa and length., the measurement of 0.05 ohms is nothing to do with the length of the main bonding conductors as I see it
it goes in the floow at front of property, (there are 3 x 10mm and 2x6mm, one 10mm being gas) one resurfaces under the sink and terminated there but i couldnt tell you if it is continuous, i mean why would you not run it continuous whenn the extension was being built!! grind my gears this does. <br>It is maybe 10-15 metre run to the water pipe in kitchen. so it obviously shouldnt be that high....so considered that, it isnt acceptable as the run is so short? or is that 0.05 only ever a rough guide. I mean 0.3 isnt really that bad surely??[/QUOTE]
You are joking with this statement I hope...
You are supposed to verify the continuity of the conductor when disconnected so it is all about the csa and length.
A 10mm² copper conductor less than 27m in length cannot be more than 0.05Ω
0.05 is considered negligible - 0.25 or 0.3 is not.
It's just that the resistance between two points should be negligible so that there is negligible potential difference between them (in the event of a fault).
0.05Ω is deemed to be negligible as nothing will have a resistance of 0.00Ω.
The fact that this equates to 16m with 6mm², 27m with 10mm² or 43m with 16mm² is not really anything to do with it.
(Although, obviously a 10mm² conductor less than 27m cannot be higher than this and in a 'normal sized' property it will be less.)
If the resistance of the pipe itself (without bonding) to the MET and all other pipes and e-c-ps were less than 0.05Ω then the protective bonding conductor would not be necessary.