Discuss Main bonding problem again in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi been to a job wants a shed wired, about fifty meters away from the house, my concern is the bonding to the services, not good and near impossible to route to within 600mm of the stop cock/gas meter, my question is could i bond the pipes at the upstairs meter? I know what the regs state but its not if not practicable to tear the house apart to do so? Tns, currently 2,5mm to the main earth, bonding same to god knows where many thanks
 
You are trying to ensure that the bonding is connected as close as possible to the place where the 0V reference starts and to ensure that no modifications before the bonding clamp can leave an unbonded extraneous part.
It is possible that the combi boiler is acceptable but not likely, however you can see the pipework run and must make the call.
 
What has the shed got to do with things then?, your post is very confusing.
 
As Richard said ^^^^^
Although its best practice to connect the bonding within 600mm at point of entry, sometimes this is not possible/practical. In these scenarios you are required to determine the best possible connection point and then make a note on your EICR.
 
Sorry lol i suppose my point being if i was to upgrade the main bonding as well as install the shed supply but am unable to access service pipes where they enter the property, or just ignore the bonding and just note it on the eic?
 
Sorry lol i suppose my point being if i was to upgrade the main bonding as well as install the shed supply but am unable to access service pipes where they enter the property, or just ignore the bonding and just note it on the eic?
You mentioned 2.5mm2 bonding conductors, is that correct?
 
I mention the plastic pipes as this can change the needs for bonding. I've been in a recent new build with plastic incoming water main that was not bonded. I did confirm the odd copper pipes under the sink etc were not extraneous and just noted it on my cert.
 

Reply to Main bonding problem again in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
879
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
883
Does a copper gas pipe, coming into the house require bonding when the pipe is being supplied by propane cylinders, via rubber hose. Doesn’t go...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock