Paul Willoughby

I have a TNC-S System (PME) , with a 100A fuse, the main Earthing conductor is 10mm, terminated in an earth block, with main bonding conductors of 10mm.
Tails to consumer unit are 25mm with 16mm earth. The Ze of main Earthing conductor is good.

British gas put an isolator last year and at the time I asked if main earth needed upgrading and they said it was standard size.

I have my part p assessment next week, so wondered If I needed to upgrade to 16mm to satisfy the inspector.

Just checking I have everything covered, thanks for any advice that conforms with BS7671


Thanks

Paul
 
The adibiatic equation will tell you mate. But if you do need to upgrade the 10mm from the head to the MET, you will probably need the DNO to come and do it.
 
It should be OK as it is, and like Jay says its up to the network operator to upgrade it. The fact that the board has 25mm/16mm means you have gone as far as you can with earthing. Maybe worth noting it on EIC in the comments on existing installation box, if its the niccy that your with they like to see that you know what that box is for.
 
I have a TNC-S System (PME) , with a 100A fuse, the main Earthing conductor is 10mm, terminated in an earth block, with main bonding conductors of 10mm.
Tails to consumer unit are 25mm with 16mm earth. The Ze of main Earthing conductor is good.

British gas put an isolator last year and at the time I asked if main earth needed upgrading and they said it was standard size.

I have my part p assessment next week, so wondered If I needed to upgrade to 16mm to satisfy the inspector.

Just checking I have everything covered, thanks for any advice that conforms with BS7671


Thanks

Paul

so there is a 16mm2 earth from the DNO block to the Dist board and the DNO supplied a 10mm2 to the block?
 
There's absolutely nothing wrong with what you have. It doesn't matter one bit that the earth is the same size as the minimum size of TNC-S main bonding conductor.
you size the earthing conductor to the most onerous condition. The adiabatic would almost certainly give you a smaller conductor than the 10mm anyway.
the OSG is not the only way you should design.
 
Sorry to 're open' such an old post.

I'm having the same dilemma and want to keep the inspector happy. The only difference with my installation is that the 10mm earth goes directly to the consumer unit from the DNO and the fuse is 60A. Is this kosher?
 
Sorry to 're open' such an old post.

I'm having the same dilemma and want to keep the inspector happy. The only difference with my installation is that the 10mm earth goes directly to the consumer unit from the DNO and the fuse is 60A. Is this kosher?

What size are the meter tails?
 
No, TNC-S. I already have but this is the first time I've seen anything less than 16mm used before. It just threw me off. So am I safe in assuming the inspector will be happy with 10mm?
 
Yes I am. It's my first one for NICEIC. I understand why we have minimum CSA's for Earths but having never seen one this small on a domestic job just threw me off a bit.

Its NOT unusual for properties to have a small link to the water pipe, or worse, no earth at all.....
 

Reply to Main Earthing conductor size. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
660
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
758
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock