Currently reading:
Max Zs /ADS / shared CPC & N

Discuss Max Zs /ADS / shared CPC & N in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hey Everyone.

Whats your thoughts on using a 3core & earth to run x 2 final circuits? I have x1 three core & earth feeding contactors for emergency lighting. L1- fed from a 6A mcb is feeding a switched pole on a NO contactor, L2- fed from a different 6A mcb also feeding a pole on a NO contactor.
At the outgoing side of the contactor is x2 em lighting circuits, done in 1 5mm T&E. Now when calculating max Zs Im essentially using the same CPC for both circuits ( in the 3 core cable), which I don't like. Is it deemed safe/ normal practice to allow these essentially 2 circuits to share the same CPC & N. The DB is very close to the contactor board, so Im planning to run x2 new 1.5mm feeds to the contactors to gain true Zs readings.
 

Reply to Max Zs /ADS / shared CPC & N in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock