Search the forum,

Discuss Max Zs on rcbo type c 32a 1667 or 0.54?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

SDSHAMMER

Has anyone any views on max Zs for say a type c 32a rcbo at 80% is 0.54 and 100% 0.68. I am currently testing a collage and all ring circuits are type c and I am exceeding 0.54 and 0.68 this is a TNCS system so to my knowledge table 41.5 in regs which tells us 1667 for 32a rcbo for TT systems but I have guys telling me this is fine for TNCS as well. I would disagree as the installation hasn't been designed properly as there is no need for type c and all circuits are wired in 2.5mm pvc singles. If type c was really needed why did they not just use 4mm pvc singles to bring max Zs down? Thoughts Much appreciated guys. Think next step is for Nicec to make final call
 
it is acceptable to use an RCD to achieve ADS when the Zs is too high for other methods.
What is worrying, is whether the test schedule will be conducted, to ensure the RCDs will operate in the event of a fault.
 
Has anyone any views on max Zs for say a type c 32a rcbo at 80% is 0.54 and 100% 0.68. I am currently testing a collage and all ring circuits are type c and I am exceeding 0.54 and 0.68 this is a TNCS system so to my knowledge table 41.5 in regs which tells us 1667 for 32a rcbo for TT systems but I have guys telling me this is fine for TNCS as well. I would disagree as the installation hasn't been designed properly as there is no need for type c and all circuits are wired in 2.5mm pvc singles. If type c was really needed why did they not just use 4mm pvc singles to bring max Zs down? Thoughts Much appreciated guys. Think next step is for Nicec to make final call


Why should NICEIC make the final call? they don't make the rules, they just take your money
 
Yes spinlindon that is my main concern. The regs don't give a definitive answer but i myself would design a circuit to meet disconnection times in event of a fault current irrespective of the protection device. Yes pete999 they are good at taking our money, making their own rules and letting anyone join them IE Cowboys
 
I fail to see why the theory that 1667 ohms can apply to TT systems when they fail to meet disconnection times, but it is not suitable on TNS/TNCS systems. Maybe not the best design in the world, but surely what's good for the goose is also good for the gander?

However, if it's all in 2.5 singles (line, neutral, and earth) surely that means if Zs doesn't comply, the short circuit (line & neutral) will have the same resistance and thus it won't comply - the RCD will deal with the high resistance in the event of fault current, but surely there's a chance the breakers won't break (in time) in the event of short circuit current?
 
Last edited by a moderator:
I fail to see why the theory that 1667 ohms can apply to TT systems when they fail to meet disconnection times, but it is not suitable on TNS/TNCS systems. Maybe not the best design in the world, but surely what's good for the goose is also good for the gander?

However, if it's all in 2.5 singles (line, neutral, and earth) surely that means if Zs doesn't comply, the short circuit (line & neutral) will have the same resistance and thus it won't comply - the RCD will deal with the high resistance in the event of fault current, but surely there's a chance the breakers won't break (in time) in the event of short circuit current?

holy fuses, batman. good thinking for so early before beer time. :stuart:
 
I fail to see why the theory that 1667 ohms can apply to TT systems when they fail to meet disconnection times, but it is not suitable on TNS/TNCS systems. Maybe not the best design in the world, but surely what's good for the goose is also good for the gander?

However, if it's all in 2.5 singles (line, neutral, and earth) surely that means if Zs doesn't comply, the short circuit (line & neutral) will have the same resistance and thus it won't comply - the RCD will deal with the high resistance in the event of fault current, but surely there's a chance the breakers won't break (in time) in the event of short circuit current?


So the next question is, are there required disconnection times for short circuit faults in BS7671! I am pretty sure it is just EFLI which it covers. 411.3.2. :)
 
So the next question is, are there required disconnection times for short circuit faults in BS7671! I am pretty sure it is just EFLI which it covers. 411.3.2. :)

But wouldn't 434.5.2 come in to play?

Just quickly done the maths on that. Can someone confirm my working for my own learning. Adiabatic says about 80 seconds to the limit, but the short circuit current will be over 400 amps which will break a type C in the required time still. So in this case it is fine and complies - can someone confirm I'm on the right tracks?
 
Last edited by a moderator:
Just redone calculations as OP didn't give us the reading he was getting. Am I right in saying any reading on ze + r1+rn greater than 3 ohms won't achieve compliance with 434.5.2? I know 3 ohms is a substantial figure, and very likely won't be this high in OPS case - just trying to see if I'm approaching this the right way
 

Reply to Max Zs on rcbo type c 32a 1667 or 0.54?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock