Discuss maximum demand, main fuse and tails in the Australia area at ElectriciansForums.net

A

adam.h

Ok, installing a new cu, leaving old one in place. They currently have 60A main fuse. With the new demand added the total MD is now 86A.

Do I just ring up the supplier and get them to change the fuse and meter tails to 25mm where needed. Can I then keep the 16mm out of the henley block to each cu as individually they are lower then 60A?
Will this be a cost to the customer or do the suppliers pay for this?

thaaanks!
 
You would reallly need to speak to the DNO about the propsed changes upgrade of tails is the customers responsibility the DNO stops at the meter unless as some do an isolator is put in then it would be the customers responsibility from isolator to CU.


Chris
 

Reply to maximum demand, main fuse and tails in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
360
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
967
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock