Discuss MCB type ratings (b,c,d) in the Industrial Electricians' Talk area at ElectriciansForums.net

D

DanBrown

Hi Guys,

I have just been on a call out to a ventillation fan within a kitchen sometime tripping out on startup.

Basically the fan runs at about 9 amp full on-load current, but the start-up it in the region of 100 amp. Could anyone tell me what rating the fan should be on, and what is if any the theory behind selecting the correct rating type of the mcb. It was on a type ''C'' 20amp that i thaught was adequate for that type of startup.

What is the theory behind selecting the correct rating....


Thanks
 
Hi Guys,

I have just been on a call out to a ventillation fan within a kitchen sometime tripping out on startup.

Basically the fan runs at about 9 amp full on-load current, but the start-up it in the region of 100 amp. Could anyone tell me what rating the fan should be on, and what is if any the theory behind selecting the correct rating type of the mcb. It was on a type ''C'' 20amp that i thaught was adequate for that type of startup.

What is the theory behind selecting the correct rating....


Thanks

ok "In" is the MCB nominal rating (say it has a In of 10A)

Type B's have an instanteneous trip current of 3 to 5 times In (so 30-50A)

Type C's are 10 to 20 times (so 100-200 amps)

Type D's are 20-50 times (so 200-500amps)

think those are the values, dont have the OSG in front of me
 
ok "In" is the MCB nominal rating (say it has a In of 10A)

Type B's have an instanteneous trip current of 3 to 5 times In (so 30-50A)

Type C's are 10 to 20 times (so 100-200 amps)

Type D's are 20-50 times (so 200-500amps)

think those are the values, dont have the OSG in front of me

I thought it was

Type 'B' 3 to 5 times

Type 'C' 5 to 10 times

Type 'D' 10 to 20 times

Have just checked in OSG Page 51 and it is as I have posted.
 
Last edited:
I thought it was

Type 'B' 3 to 5 times

Type 'C' 5 to 10 times

Type 'D' 10 to 20 times

Have just checked in OSG Page 51 and it is as I have posted.

I am not even going to check Ian, and the book is in front of me:p

I was 'off the cuff' when i wrote the figures down

thanks for the correction:)
 
hi
i would suspect the fan ,or at least where its air is coming from ,or going to ,i check everything else first ie ,loose connections,then"megger the motor", check the fan on the motor as well ,its probably clogged with grease,
good luck
 
Check the trunking that the fan is in as if it has not been cleaned for ages it counld be that blades are jamming on the congealed grease which will be in the trunking with it being in the kitchen.
 

Reply to MCB type ratings (b,c,d) in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
877
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock