Discuss Memshield 2 board in the Australia area at ElectriciansForums.net

S

SimpleSimon

So, today I'm being put with a job by a manager who I don't think fully knows what he wants me to do.:confused5:.
In March I did a periodic inspection on a distribution panel that failed due to numerous circuits having low IR. This panel was located in a plant room, which also holds an irrigation tank at a sub level.

Now it's come back that he wants the board changed but not because of the failed circuits, he believes its not IP rated enough for the conditions of the plant room. The board is a Memshield 2 metal clad, all blanks are in (as I did it myself.) and all horizontal and vertical IP ratings are correct. I don't feel this needs upgrading, it's IP55 and the room can be prone to cool temperatures. He says it's prone to moisture (which I cant see!!) and flooding, but the board is above waist height and there's never been any record of flooding that high. So I'm saying no to the board change and concentrate more on the faulty circuits as at the moment they're all isolated and a certificate cant be issued until these are rectified!!
Just wanted anyones thought's on this :)
 
i'd agree with you on this. what's the point of changing a perfectly good board. ask your monkey (sorry, manager) if as he says, it's liable to flood, can he source an IP68 board.
 
Thing is it won't be liable to flood as there is going to be a new sup pump installed in there as well. I've seen the spec they've given the client saying ' Installation of correct weather proof panels which will require re-wiring and re-cirtifcation.':icon_bs:
 
Simon you can not go wrong mate if you obey the last order mate, which is this case was to change the board, look at it this way you could be 25mts up changing floodlights, or down a hole changing a sewage pump, if the managers wants a new board then the manager gets a new board .................... and if dosen't clear the low readings then ........what is the next order guv ?
 
Very true Malcolm. I don't want to sit and have a big arguement but I will put my point across and if he doesn't want to listen, what more can I say!!
 
Well noone could get hold of the manager in question he's off for personal reasons (real personal reasons feel sorry for the man) so I ended up tidying the steel trunking as there are redundant cables coming out of that so at least there was something for me to do and researching anti-condensation heaters for distribution panels.
 

Reply to Memshield 2 board in the Australia area at ElectriciansForums.net

Similar Threads

Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
3K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Due to an increase in load for a subman, I now need 2 phases for an outbuilding. Original design was 63a supply, but now an electric shower and...
Replies
23
Views
3K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
917

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock