Does anyone know if there is a common problem with the Merlin Multi 9 RCCB 4 pole 100Amp 300mA, not tripping as we have replaced an existing unit with a new one but the issue is the same,

Many Thanks

Mark
 
Have they disconnected all loads from the RCD?

Are they testing on the load side of the RCD?

Have they tried to test it with a temporary test lead connected to it? As sometimes they wont test directly on to the terminals.
 
The unit is still situated in the Dis Board, they have tried the test on one of the local circuits (kitchen ring main),

No temporary leads will have been used,
 
Well its worth trying it by disconnecting the loads directly on the terminals if that fails make a short testing lead up and try that.
 
My gast is flabbered, how in the name of god can anyone fall for that one?

For those with no grasp of the English language gast & flabbered equates to flabbergasted. Look it up in the OED.
 
So has the Electrician now refitted the original one back in as i suspect their was nothing wrong with that one either or is he now going to rip the customer of replacing a part that probably was ok.... had he known what he was doing in the first place the customer wouldn't have been lumbered with an extra cost.

Im also Ghastly flabbered!
 
So has the Electrician now refitted the original one back in as i suspect their was nothing wrong with that one either or is he now going to rip the customer of replacing a part that probably was ok.... had he known what he was doing in the first place the customer wouldn't have been lumbered with an extra cost.

Im also Ghastly flabbered!

Now why did that go through my nasty suspicious mind?
 

Reply to MERLIN GERIN Multi 9 4P RCD RCCB 100A 300mA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock