Hi,

My new leakage tester arrived so I wanted to try it out, I connected it to the Line and Neutral meter tails and got a total leakage with all circuits on of 8.05 ma, I turned them all off and re-tested individually and found that the first floor ring final was giving the highest leakage of 6.34 ma

I wanted to see how this result compared to an RCD ramp test so I turned all circuits off and connected direct to the RCD and it tripped at 24ma, I turned the ring final circuit back on and re-tested and to my surprise I got the same result of 24ma??? Indicating that I have no leakage which is not true.

The tester is a Fluke 1653 which is not long back from being calibrated.

BTW: The new Metrel 9272 is a fantastic bit of kit and I cant wait to use it fully.

Any ideas?
 
Last edited:

Reply to Metrel MD9272 Leakage testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock