ok cool, this will be the second attempt,
i have a circuit tested to be too high Zs Values for the existing protective divice, its an addition to an existing radial circuit, however the new addition is protected by a 13a spur, the max permitted Zs value for the BS1362 is acceptable.


my question is this! is it acceptable to use a BS1362 as the circuits overcurrent protective device for the modified circuit when completing a minor works cert, cant say I have never given it much thought until now????
 
Last edited by a moderator:
OK so the extra part of the circuit you have added from the 13 amp FCU sounds acceptable as long as the BS 1362 fuse will disconnect the circuit in 0.4 of a second the problem you have is that you have fitted the 13 amp FSU on the circuit that the OCPD supplying that needs to disconnected the circuit within 0.4 seconds if is does not then it is unsafe , If there is 30mA RCD protection you may be able to get away with it , but it Is not good practice just the really on an RCD for fault protection
 
looking at it logically, if the 1362 fuse will diss. in 0.4 secs for the extension part of the curcuit, and the Zs at the FCU is within the max. for the OCPD at the origin of the circuit, then it should comply. tin hat firmly on.
 
I agree with you Tele but if the Zs at the FCU is to high for the OCPD for that circuit then the OP has a problem

hi thanks for the reply, yes the Zs is well within at the point of the spur, its just the new circuit which is high, it will require investigation but should do for now.
 
so if its a new cicuit ,not an addtion or modification to a circuit then an installation cert may be required
Athough even saying it ,an eic seams over the top for such a small job , but thems the rules

I think the definition section of bs7671 is required here. Think it says a circuit starts at a fuse board our similar
 
Can't see any problem with that at all. list BS1362 as OCPD and list cable size from the load side of spur. If Zs is low enough for fuse rating and cable protected then it is definately ok.
 
hi thanks for the reply, yes the Zs is well within at the point of the spur, its just the new circuit which is high, it will require investigation but should do for now.
Yes as you say may nead investigation to find if the Zs is is high due to a poor connection or if infact it is similar to the calculated value for the characteristics of the cable you have installed if the test reading works out to be correct then it sounds to me that there is nothing wrong with your installtion andyou can fill in the minor works as you suggested
 
What I have done before is list the protective device (e.g. BS 1361 HRC fuse) for the circuit on the Minor Electrical Installation Works Certificate, then in the box asking what work was carried out I will declare that it is connected to a Fused Connection Unit protected by whatever rating of BS 1362 fuse, and that the maximum Zs for 0.4 second disconnection is whatever (depending whether 3A or 13A).

Then there really can't be any comeback as you have clearly explained this on the Certificate.
 

Reply to minor works high Zs Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Evening all, I just wanted to see if electrical improvers/adult trainees with appropriate levels of experience and who hold testing...
Replies
0
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
810
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock