Simon_

I have upgraded an old wylex CCU to modern and removed the separate Isolator box with a 40a rccb that was connected to a Henley block and then powering the shower from the CCU. The cable is 6mm and it's a Mira sport but fairly old. There was no shower switch so it was permanently on all the time and some of the cable was run on the outer wall of the house and back in the brick. Length from CCU to shower is approx 10-15m and obviously now a switch will be put in just before the bathroom. Was the Mira sport a specific kw to that model? It says on some sites that it's 10.8 kw in which case it will need a 10 mm cable and 45a mcb as it has a 240v sticker on the inside. I.R. Test on the old cable came back fine.
 
Was fitting a new switch and checking over the Shower circuit part of the CU change?

If it wasn't I would be clamp testing the shower to get a "working" reading and depending on what you get would be my next step. If it is running on max over that 40amp protection device rating, then I would be advising the client that I'm switching the circuit off as it contravenes reg 433.1.1 and note it on your EIC under existing installation and you have isolated the circuit.
 
Yeah fitting the new switch and cable will be part of the cu change. The installation has not been re-energised yet since being installed.
 
Well then you now have the responsibility of the circuit.

You can not energise the circuit if the appliance is pulling more than the load ie 40amp protection device pulling 42 amps as in reg 512.1.2 the equipment must be suitable for it's design current, so a 42amp appliance is not suitable for a 40 amp protection device.

As I suggested I would clamp the unit of maximum power and see what you get. If it is below the 40amp then yes energise the circuit, but make a note on your EIC about existing installation, if it is above 40 amps then you really have no choice but to isolate the circuit and advise your client what to do

1 upgrade the circuit
2 fit a smaller shower.
 
As you have found there are 6 models in the range, the Mira Sport 7.5, 9.0 and 9.8Kw, plus the Mira Sportmax 10.8Kw, plus the Mira Sport Thermostatic 9.0 and 9.8Kw. As you have an older model it's likely to be one of the basic Mira Sport models, most likely a 7.5 or 9.0Kw model.
If you remove the shower unit front cover you will find the units rating label, remember when calculating the nominal current demand that elements are rated at 240V (NOT 230V) so that should be the divisor in your calculation.
 
Last edited by a moderator:
I quite sure the Mira Sport is 9kw. What type is it as there are 2 or 3 variations? The newer has the control knobs one above the other and the older type side by side.
 
I think an upgraded circuit would be best. I've just found the factory sticker on the shower and it's definately a 10.8k. The cu is crabtree but they don't make a 45 amp mcb, think I'll have to use a 50a mcb with the 10mm.
 

Reply to Mira shower help/ ratings please in the Australia area at ElectriciansForums.net

Similar Threads

Hi Im newto this forum and hello to everybody. Im experienced electrician with 15 years of experience in all kind of domestic premised. Some...
Replies
42
Views
6K
Morning.... I was wondering if you guys could help me with this..?! I’m currently having my kitchen updated, including all new appliances... The...
Replies
5
Views
1K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K
Hi All. Hope someone can help here as I'm confused with all the info floating around all over the net. Our shower blew its PRD last night and we...
Replies
19
Views
2K
Hello Looking for some guidance please. Lived in current house just over a year now and had couple issues with our pull cord switch (45A)...
Replies
49
Views
5K
Deleted member 9648
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock