Discuss Mono Water Pump Cabling in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

O

Ohm From Ohm

Hello,

Can anyone please assist me in the following:

My client wants to feed a Mono water pump from a distance of approx. 360 metres.

I have a choice of using PVC/PVC cable taped to a catenary wire. I am not happy with this method and would prefer to run PVC/PVC/SWA cable underground. The pump is rated at 186 watts S/P.

Can anyone advise the voltage drop if the following cable is used.

2.5mm PVC/PVC 6242Y
1.5mm PVC/SWA 2 core 6942X
1.5mm PVC/SWA 3 core 6943X
or 2.5mm PVC/SWA 3 core 6943X

I recently retired and gave my regulation books to an apprentice, and I obviously don't remember the M/V amp figures etc. This is a private matter for a relative.

Much appreciated.
 
1.5mm is 29mV/A/m
2.5mm is 18mV/A/m

so @ 186watts = 0.8A

vd for 1.5mm = (29 x 360 x 0.8)/1000 = 8.3V.

with all due respect, how old are you, as you say you're retired? i'm thinking about it, but i'm only 70. how soon do you think it's time to give it up?
 
The volt drop during start up is going to be the problem with a single phase pump, depending especially on the cycle times of the pump. I don't have the info to hand to do the calcs but gut feel says I'd probably be looking at a 4mm supply on a 360m run.
 

Reply to Mono Water Pump Cabling in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Recently a couple of threads have discussed T&E cable and it became apparent to me that the 2.5mm, which I have only ever seen as solid core, is...
Replies
47
Views
6K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
545
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Iv been asked to wire a separator (portable to go to different farms and separate water from slurry) to a 3phase 40 kva generator. The separator...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock