Discuss Moving Consumer unit in the UK Electrical Forum area at ElectriciansForums.net

AdieB

-
Reaction score
6
I have to move a Consumer unit approximately 6 mts. Had suggestion buy NAPIT technical to fit enclosure with terminal rail and terminals and then extend cables to new consumer unit. As the enclosure will not be readily available the terminal method would not be Maintenance Free. (If there was a problem in the future access to the enclosure could be achieved but would make a mess of decoration) Is there a Maintenance Free enclosure that will take multiple cables on the market? Or is it multiple J803 and the like. Anyone done something similar?



AdieB
 
You have all the Qualifications needed the Adie what are they exactly?
 
I had to extend an installation replacing a consumer unit last week. Not quite that long, but I used Wagoboxes, installed in maintenance free mode (i.e. with required de-rating and ensuring maximum aggregate current was not breached as I used one box for a couple of circuits) in an accessible location (in the ceiling void above the CU) and documented it on the EIC for the work.

And I concur with Midwest... if it's got screws in it, it should be accessible.
 
Even with Wago cage clamp connectors (there're other manufacturers), the enclosure should be accessible IMO. If this is not achievable, look at other methods as SparkyChick suggested, or partial rewire of feeds to RFC, Radials etc.

Anyhow, my soufflés are in the oven, and I'm just have 5 mins before I need to prepare my Béarnaise sauce for my Chateaubriand. We having fried Mars Bar for pud. :)
 
I have to move a Consumer unit approximately 6 mts. Had suggestion buy NAPIT technical to fit enclosure with terminal rail and terminals and then extend cables to new consumer unit. As the enclosure will not be readily available the terminal method would not be Maintenance Free. (If there was a problem in the future access to the enclosure could be achieved but would make a mess of decoration) Is there a Maintenance Free enclosure that will take multiple cables on the market? Or is it multiple J803 and the like. Anyone done something similar?



AdieB
Where do you intend to fit the extension box?
 
I have to move a Consumer unit approximately 6 mts. Had suggestion buy NAPIT technical to fit enclosure with terminal rail and terminals and then extend cables to new consumer unit. As the enclosure will not be readily available the terminal method would not be Maintenance Free. (If there was a problem in the future access to the enclosure could be achieved but would make a mess of decoration) Is there a Maintenance Free enclosure that will take multiple cables on the market? Or is it multiple J803 and the like. Anyone done something similar?



AdieB

Hum.......
 
Metal enclosure, DIN rail Wago connectors, or DIN connectors
If you absolutely have to have it non accessible due to decoration and all, I would go with Pete's idea as Wago on a DIN rail will be maintenance free and the non combustible enclosure will take care of the other regulation requirement. Just make top job of it and document it well with photo on EIC.
 
Asked my Scheme recently, their opinion on such an enclosure as to whether it would be classified as 'similar switchgear', as described in reg 421.1.201.

''This will be the decision of the designer but it would suggest based on our guidance in this situation the enclosures and connections do not fall under 'similar switchgear''.
 
Asked my Scheme recently, their opinion on such an enclosure as to whether it would be classified as 'similar switchgear', as described in reg 421.1.201.

''This will be the decision of the designer but it would suggest based on our guidance in this situation the enclosures and connections do not fall under 'similar switchgear''.
Good bit of buck passing by your Scheme there Middy
 
You have all the Qualifications needed the Adie what are they exactly?

I am of the older generation. I have A B & C and 17th Edition City and Guilds I also have the inspection and Test certificate and have been in the electrical industry since 1973 when I did my indentured apprenticeship. I am a also registered with NAPIT.
 
The meter has already been moved and new tails installed . In the meter box due to the length of the tails an 100A isolation switch has been fitted.
 
The meter has already been moved and new tails installed . In the meter box due to the length of the tails an 100A isolation switch has been fitted.

Is that a switch fuse with a 100A fuse or just an isolator rated at 100A? If the tails are over 3m it will need to be a switch fuse.
 
The other option which nobody has mentioned so far is soldered or crimped joints with a liberal application of suitably rated heat shrink sleeving. Just a thought.
 
The extension box is in place of the old consumer unit. the cables will then extend to the new consumer unit location
In that case the connections would be accessible wouldn't they? ergo no need for MF connectors.
 

Reply to Moving Consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
5K
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
1K
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock