Discuss new supply needed for granny annex? in the UK Electrical Forum area at ElectriciansForums.net

S

sparks1664

I've been asked to quote for wiring a granny annex and i'm in two minds whether it needs a second supply or not, i know the on site guide is only a guide and you have to do whats practical but because there's a real possibility of cookers, kettles dishwashers etc.. being used at the same time i'm thinking it would be better on a separate supply, wiring as follows

x2 - 32A cookers
x3 - 32 rings
45A garage/shower (used daily)
15A immersion
6A lights
6A lights

I get about 153A after diversity

what would you do?
 
Out of interest what is the heating system? If you could swap that shower to a mixer it would help improve the loading situation.

I'd weigh up the cost of an extra supply to that of changing the plumbing.

I still reckon the single supply will more than cope with that demand anyway. How did you calculate the shower and cooker? Seems high
 
heating's on a combi , one cooker is 4.5kw the other 10.5kw. first 10A plus %30 of rest. i calculated shower as 100% with a few sockets/lights in garage, i have suggested changing shower, how did you get 60A?
 
NO property would EVER draw 163 a...

The diversity calcs in the OSG are so old hat and take absolutely no account of the reality these days....

Even multiplying by 0.25 will give you 58A but that is too high.... IMHO
 
6 bed holiday cottage, 3 electric showers, cooker etc. First I was suprised when the seals fell off, second I was suprised when the fuse fell out, third I was really suprised to find that it had all been running quite happily for over 10 years on a 60A fuse. I worry a lot less about maximum demand these days and would agree with all the others
 
There is a 12 bedroom guesthouse local to me with an electric shower in each room. The property is fed with a standard single phase supply and the client assured us he had never had an issue! Was tempted to pull the fuse carrier and see if there was actually a fuse in there!
 
There is a 12 bedroom guesthouse local to me with an electric shower in each room. The property is fed with a standard single phase supply and the client assured us he had never had an issue! Was tempted to pull the fuse carrier and see if there was actually a fuse in there!

They serve breakfast by room numbers at ten minute intervals so only a couple of showers at most can ever be on simultaneously. :D
 
They serve breakfast by room numbers at ten minute intervals so only a couple of showers at most can ever be on simultaneously. :D

Possibly! They take a lot of these minibus tours so most, if not all rooms being filled at the same time of evening. Can only be luck that they've managed so far.
 
I've been asked to quote for wiring a granny annex and i'm in two minds whether it needs a second supply or not, i know the on site guide is only a guide and you have to do whats practical but because there's a real possibility of cookers, kettles dishwashers etc.. being used at the same time i'm thinking it would be better on a separate supply, wiring as follows

x2 - 32A cookers
x3 - 32 rings
45A garage/shower (used daily)
15A immersion
6A lights
6A lights

I get about 153A after diversity

what would you do?

As mentioned if new shower was mixer type then you can cross off the shower and immersion, then you're sorted.
 
heating's on a combi , one cooker is 4.5kw the other 10.5kw. first 10A plus %30 of rest. i calculated shower as 100% with a few sockets/lights in garage, i have suggested changing shower, how did you get 60A?

If they are having a combinboiler then why have you allowed for an immersion heater?
 
I think he's included the two ring mains from the main house, and I'm assuming the immersion is in the main house. Could be wrong.
 

Reply to new supply needed for granny annex? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
2
Views
126
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I'm converting my old garage into a two bedroom annex. At its nearest point it is approx 10m from main house. I plan it to be all electric, UFH...
Replies
5
Views
3K
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
670

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock