I've been asked by a customer to remove four nights storage units and replace the switched fused spurs with single 13amp sockets.
Each unit is fed from a dedicated consumer unit supplied from a economy 7 meter.
I need to remove the meter tails from the night tariff meter and connect the consumer unit that feeds the replaced spurs through the Henley blocks that feeds the main consumer unit.
Is this practice reportable under part P and does the electrical supply companies need be informed.
 
If the off peak tariff is no longer being used I would recommend talking to the energy supplier as usually the normal tariff is more expensive when a split tariff is being used. So they may want to change the meter.

If you need to remove the tails from the off peak tariff meter this will mean cutting the seals and if they choose to change the meter they will know what you have done.

As far as Part P goes I think yes it is notifiable as it is a major modification.
 
Ist point of contact for the Customer is the Energy supplier.
They need to know and agree to drop the E7 charges.

It may be that they'll leave the existing meter in and charge the same rate for both tariffs for now, then no tail shifting required.
Or if they want to change the meter then they'll have to move the tails.
 
The householder should have a single point of isolation, the service fuse will not suffice.
 
The energy provider should do the conversion. It is their equipment, when I change from E7 to standard, e7 tails are disconnected put in blocks, meter changed to single tariff, then its over to Electrician to reconnect to 24hr supply.
 
Have not enough room to install single point isolation.
Cannot find any regulation that covers this.
Would signage surface
Reg 537.1.4, signage may apply to large commercial/industrial sites where multiple supplies are present but see no excuse on a domestic. Will the sockets have rcd protection.
 
"537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply."
 
"537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply."
Reg 537.1.4, signage may apply to large commercial/industrial sites where multiple supplies are present but see no excuse on a domestic. Will the sockets have rcd protection.
No they will not as i will not be changing the consumer unit.
The only other way i can see around this is to supply the old ecconomy 7 consumer unit from a 32 amp mcb on the main consumer unit with 6mm t&e which has a double pole switch disconnector and a 30mA rcd and this should cover all the regs?
 
You are going to have to provide additional rcd protection because you are creating new socket outlets. The best way to do this is to replace both boards with a single unit.
 
What you need to do, is get the DNO to remove the off peak meter and to have ready a dual isolator for them to connect the meter tails into.
Then you can connect both CUs into the dual isolator.
As Westward10 says, you will need to provide RCD protection for the sockets.
 
What you need to do, is get the DNO to remove the off peak meter and to have ready a dual isolator for them to connect the meter tails into.
Then you can connect both CUs into the dual isolator.
As Westward10 says, you will need to provide RCD protection for the sockets.
Problem here he is missing rcd protection with the existing board, suppose you could fit rcd sockets.
 

Reply to night tariff meter change to standard tariff in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
386
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
555
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
845
Hi everyone, a landlord is converting a house into two flats and wants a separate consumer unit for both flats upstairs and downstairs. He also...
Replies
13
Views
1K
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock