- Reaction score
- 7,755
what would you put on test sheet r1+r2 no earths
Discuss no earth on lighting r1+r2 what do you put on sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Yeah I take no cpc, but you have a point. Not clear is it.Is not very clear now I have reread it, is he saying there are no cpcs or no earth continuity.
No I immediately assumed no continuity till I read your post. Can you clarify please OP.Yeah I take no cpc, but you have a point. Not clear is it.
OP does the cable have a cpc?hi on testing on earths what would you put on test sheet eicr
We will get there on the end!OP does the cable have a cpc?
Are there cpcs from the dist board and none at accessories or a total absence of them?no not one. sorry this for lighting cable only
Okay you can not test for the obvious, this is a EICR, I would give it a code3 at least, if metal accessories etc code2.no not one. sorry this for lighting cable only
Right okay on the schedule it will be NA because you can't give a reading if there is no conductor to give a reading for, even though NA is self explanatory the schedule should explain this. See Daves post for Coding recommendations, light switch back boxes also need earthing unless they are plastic or have nylon fixing points.none at cu and none at the accessories
See Post 12 on this thread.just one on question which dave has coding recommendations
Reply to no earth on lighting r1+r2 what do you put on sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.