somersetsparks

-
Esteemed
Reaction score
706
Hi all,
Been a few years since i've posted but here goes! At the factory I work in we have an old Spanish line from the mid-eighties that is fed from uk 400v 3 phase via a 3ph step down autotransformer to give 380v output.
The spanish panels Do not use a neutral, just 3 phases and further 380v -> 220v ( 110v - 0 - 110v) transformers to provide single phase power to some circuits.

Recently we have had a replacement 30kW Mentor MP DC drive fitted in one of the panels (replacing an old Simoreg analogue DC drive due to failure, ever since fitting this drive we have had issues with it tripping on a hardware fault and occasionally taking out the 100A line fuse (supplying the said DC drive only) on L2 (I am told this also happened before with the old drive). I am aware that the fuses are overrated anyway, and to have an instantaneous blow means a lot of current possibly a motor flashover !?,

Anyhow, today I was told that this drive trip occurs several times a day and is reset by the line manager, I have checked the supply voltage before and after the autotransformer and found that L2-L3 (Outgoing side only) sometimes dropped to 60v under full load for a couple of seconds at a time! I have tested the autotransformer windings and found no issues, however I have found that no supply neutral is connected, leaving it as a floating Y-Y autotransformer, we have 2 more of these transformers on different parts of the factory and both have the incoming neutral connected to the star point, could this be my issue? (this line was not originally ours it was purchased second hand and installed by contractors)

apologies for the very long post, any help much appreciated!
 
Last edited:
I looked up 30kW Mentor MP drives and found this information:

4.3.1 Supply types Drives rated for supply voltages of up to 575 V (rated up to 210 A) and 600 V (350 A and above), are suitable for use with any supply type i.e. TN-S, TN-C-S, TT, IT with grounding at any potential i.e neutral, centre or corner (“Grounded delta”).

See: http://www.dcdrive-direct.com/media/18931/Mentor_MP_User_Guide.pdf

It does seem that the 380Volt 3 phase 3 wire supply to the drive can be derived from a 3 phase 4 wire system which has an earthed neutral (ie: TN-S and TN-C-S and TT). As you mention, the current drive has supply from an autotransformer with a floating star point ie virtual neutral( - at some potentials with respect to earth and supply neutral) albeit not required to be connected to the drive. The other two drives do have their star points connected to neutral. So based on this information it seems odd the auto-transformer you mention does not have a 4 wire supply and the star point connected to neutral which would fix its potential to the supply neutral.

Hope this helps in some way.
 
Some further thoughts. The magnetic core of a transformer does not have a linear B/H curve - think hysteresis curve. This means(see * below) that a zero sequence current (with higher order odd harmonics - 3rd, 5th etc - which add up) 'need' to flow in order to produce a sinusoidal excitation field and thence sinusoidal secondary voltage. In a three phase star wired system this requires a neutral current to/from the star point. So the the absence of the neutral connection to the star point may be causing distortion of the voltage waveforms at the output of the A/T and hence troublesome currents large enough to rupture fuses.

*(Whenever a sinsusoidal emf is applied across a non-linear component the current which flows has the fundamental and harmonics of it, their ratios being dependent on the nature of the non-linearity).
 
somersetsparks - If after all the appropriate continuity, insulation, connection checks of the drive and the auto-transformer you find nothing untoward then I recommend you connect the star point to the neutral of the supply's source of electricity.
 
Hi marconi, thanks for your reply, it's been a while since I've thought about it, but I don't think it would cause to many problems if I connected the supply Neutral to the auto transformer, as shown in part of the link you have posted, we would then have somewhere for the zero sequence current to go, I'm back in on Monday and will probably try it Monday night ready for Tuesday! Thanks for all your replies, it's been a real headscratcher of a fault, mentor/emersson have been helpful over the phone but it seems to be a supply fault, anyway, fingers crossed, I'll let u know how it goes!
 
Hi all, happy new year and apologies for the late reply, we have cracked the issue, it was sort of related to lack of neutral at the transformer although the voltage drops were also a symptom really.

First of all, I connected a neutral to the supply side of the auto transformer (although obviously the supply Neutral and the load neutral are the same, it is important to note that none of the loads in the panel use a neutral and all loads are connected three phase or accross to phases). After connecting the neutral my issue nearly resolved itself, the voltage stayed much more stable, and we no longer blew any fuses although the drive still tripped with the same fault on occasion although probably 80% less.

Fast forward four months and we have been living with the problem in its much reduced state, I didn't call it a success but production were pretty happy as downtime was reduced.
HOWEVER... We developed an unrelated armature/commutator breakdown after a period of excessive load on the motor due to increased hours, speed and general abuse of a 15kw dc motor.

Whilst diagnosing that fault and being in contact with Control techniques, we came accross another issue, the line reactor for this drive was undersized at 40uH instead of the recommended 220uH, this came about as the old drive had an internal line reactor so only required a small external one. When the drive was replaced with a mentor MP, the old undersized reactor was left in place.

After having replaced the reactor we haven't had a trip since!

Thanks for your help Marco night and I'm glad to have found a full solution
 

Reply to No Neutral at 3 phase step down autotransformer? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
536
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
646
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
275
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
656
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock