Hi all,
I recently carried out an EICR on a biolabs, it has a DB in the mains room that was wired direct into the busbar on 25mm tails within 3M. The busbar is on a 200A fuse and the DB in question is a 24 way three phase board.
I know that 20 + years ago when this was installed some guy has probably done his calculations and determined that this may not reach the full loading of the circuits originally installed and deemed it ok by diversity. I don't think I would personally replace overload protection with calculations, but this is what is here now.
There has obviously been additions over the years, there are multiple ring mains, heavy loads of fluorescent lighting in constant use, electric water heaters and 32A Commando Socket supplies and misc others. I think the potential is clearly over and beyond what these tails are capable off for a prolonged load.
I'm about to send a quote for a new 100A TPN Eaton switch fuse for it, along with the other remedial works, but just wanted to be sure of my thoughts and solution by running it past some of you. That way when some suit challenges why its costing them so much to get a satisfactory report I will answer with confidence!
I recently carried out an EICR on a biolabs, it has a DB in the mains room that was wired direct into the busbar on 25mm tails within 3M. The busbar is on a 200A fuse and the DB in question is a 24 way three phase board.
I know that 20 + years ago when this was installed some guy has probably done his calculations and determined that this may not reach the full loading of the circuits originally installed and deemed it ok by diversity. I don't think I would personally replace overload protection with calculations, but this is what is here now.
There has obviously been additions over the years, there are multiple ring mains, heavy loads of fluorescent lighting in constant use, electric water heaters and 32A Commando Socket supplies and misc others. I think the potential is clearly over and beyond what these tails are capable off for a prolonged load.
I'm about to send a quote for a new 100A TPN Eaton switch fuse for it, along with the other remedial works, but just wanted to be sure of my thoughts and solution by running it past some of you. That way when some suit challenges why its costing them so much to get a satisfactory report I will answer with confidence!