That table is unlikely to be of any use as it is for a conductor operating temperature of 90C, the DB incoming terminals will almost certainly be rated for 70C operation and so the conductor operating temperature must be limited to 70C
I know it also states the correction factors for different temperature which is why I posted both
 
I have that same PDF and it doesn't give conductor operating temperature correction anywhere. It only gives correction for ambient temperature.
You are correct Dave my mistake I've misread it.
It does state that the ccc ratings given in the tables are based on 90 degrees tho.
Even the biggest panel board I've fitted with a 200amp mccb the terminals were only rated at 75 degrees max.
I've never come across anything that requires 90 degrees operating temperature.
Industrial perhaps?
 
I have come across this in old factory installs a few time and in one case main fuse protecting the bus bar have been a 400amp and the same set up as the op I have always flaged these up as code 2 observations, and agree with op that fitting a switch fuse is the best option , unless there is enough room to replace the main switch with an mccb as daves says, the problem with that is you normaly nead an expansion box on the bottom of the DB to fit the mccb in , so may not be as straight forward
 
I know it also states the correction factors for different temperature which is why I posted both
Tri-rated cables require grouping factors the table you show is for a single conductor in free air. Four conductors together into the DB require a factor of 0.65 applied to this table.
 

Reply to No Overload Protection on DB wired to Busbar in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
702
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock