  1. Zdb
    Offline

    Zdb Regular EF Member

    Location:
    UK
    If for whatever reason you can't do an R1+R2 test on a ring final circuit (unable to identify opposite legs). There's also an option on the paperwork for the R2 value...

    Am I correct in thinking that you do an end to end test on the CPC's which would give you r2, then just divide it by 4 to give you R2?
     
  2. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Yes but what about your continuity tests end to ends on the ring final?
    If it's periodic testing then just take the zs at each socket.
    If it's initial verification then continuity needs to be established/verified so R1+R2 shouldn't be an issue.
     
  3. Pete999
    Online

    Pete999 Trusted Advisor

    Location:
    Northampton
    no because you will not have cross connected and tested the RFC correctly, why the difficulty in identifying the RFC legs?
     
    • Old Old x 1
  4. Zdb
    Offline

    Zdb Regular EF Member

    Location:
    UK
    It's just a minor works (socket replacement).
     
  5. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Just test zs and just to ease your mind do continuity check at the socket your replacing end to end of conductors, unless it's a spur.
     
  6. Zdb
    Offline

    Zdb Regular EF Member

    Location:
    UK
    I did continuity of L, N & E at the D.B. I just didn't want to leave a box blank.
     
  7. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    So how come you can do R1+R2 if you've already done end to end readings on the live and cpc especially?
     
  8. Zdb
    Offline

    Zdb Regular EF Member

    Location:
    UK
    Yeah you're right I'm being stupid again aren't I
     
    • Like Like x 1
    • Funny Funny x 1
  9. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Haha long week?
     
  10. Zdb
    Offline

    Zdb Regular EF Member

    Location:
    UK
    It's not even over yet lol
     
    • Like Like x 1
  11. westward10
    Offline

    westward10 Please don't bore me with your life story. Electrician's Arms

    Location:
    Northamptonshire
    Not till the fat person squeals.
     
  12. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Edit But yeah doing end to end on live and cpcs added and divide by 4 should give you total value of R1+R2 as you have 2 middles which can be considered the end of the circuit if it was a radial and 2 conductors in parallel
     
    • Like Like x 1
  13. Zdb
    Offline

    Zdb Regular EF Member

    Location:
    UK
    Thanks for the replies.

    Always appreciated :)
     
    • Like Like x 2
  14. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Following on from the above question consider a situation where you can't readily disconnect the cpc at any point to test it, or doing so is rendered largely pointless by the installation method.

    I'm thinking of a circuit wired in SWA, MICC or steel conduit/trunking.
     
  15. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Your total R2 resistance you mentioned earlier would be your end to end continuity of the cpcs you'd have measured
     
Loading...
Similar Threads - Obtaining value Forum Date
2 methods of obtaining Ipf? Electrical Course Trainees Only Apr 8, 2017
ECS Gold Card obtaining Electrical Courses & Electrical NVQ's Sep 10, 2016
Lighting Circuit r1+r2 values. Electrical Forum Jul 17, 2017
Understanding Zs values Electrical Wiring, Theories and Regulations May 8, 2017
High Zs value with 2 sockets Electrical Forum Mar 11, 2017
R1+R2 Values Periodic Inspection Reporting & Certification Mar 9, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job