So the back ground to the situation.

Gas /boiler mate replaces boiler and relocates it by about 2 meters.

Old cabling to boiler :

L, N, E and SL

New cabling to boiler:

L, N, E and SL - so cable just extended.

This is where it gets interesting:

The tank is a Megaflow, it has a tank stat, the SL from the tank stat goes to a Megaflow thermal cut-out connection (rather than back to the boiler & Megaflow have told me NOT to bypass it). At the thermal cut-out the connections are also to a Megaflow 2 port motorised valve (well actually its a Sunvic SZ 2302)

Here is a link showing the thermal cut-out etc wiring (about 1/2 way down).

http://interpart.partsarena.eu/System/DATA/Dx/DS1/installation/2978/I48-2978/I48-2978.htm


My problem is that the grey at the auxiliary switch is PL and whether the switch is open or closed it remains a PL connection. As the motor turns the valve there is a click and the voltage drops momentarily. I tried to call Sunvic technical but they go home at 4.30 so 4.55 was a bit late

So the Orange remains PL rather than SL and thus the boiler has a SL which is pretty much PL all the time.

The Gas/boiler man has changed the valve twice!

So can I please call on the collective knowledge of you good chaps, to point out the error in my thinking/understanding.

Tin hat well and truly on!

Here are some photo's of relevant bits:

Kate 1.jpg

Kate 2.jpg

Kate 3.jpg
 
I'm not familiar with the sunvic valve. Normally closed from the cylinder thermostat should go to one side of the thermal cutout, other side of cutout should go to the brown of the valve. Grey of the valve is permanent live, blue neutral and the orange is the switch live to the boiler which also is connected to the pump. I take it there's another valve? If there is, is it a two port or 3 port valve?
 
As above - Grey is PL, and Orange SL, if Orange is PL also then i suspect a duff micro switch, but seen as its been changed twice id be surprised its that.
 
Something strange there Murdoch.
The Megaflo manual shows a 2 port valve yet the drawing you've posted for the SZ 2302 would seem to indicate a 3 port valve because it has an input for hot water and central heating.
You need to talk to the plumbers to find out if the changed anything other than move the boiler.
 
will check but I'mm 99% sure the boiler has a pump in it.
there will still be a pump in the system for the Heating even if the hot water Is gravity fed which if it is then it's a bit naughty of the plumber as it should of been upgraded to fully pumped when the boiler was changed under part L. Is there only the one valve?
 
there will still be a pump in the system for the Heating even if the hot water Is gravity fed which if it is then it's a bit naughty of the plumber as it should of been upgraded to fully pumped when the boiler was changed under part L. Is there only the one valve?

2 valves. the CH works ok when i disconnect the SL from the water!
 
So, if it's a 2 port valve then it looks like the feed from the tank stat (S/L) goes to the brown, and orange to the boiler. You do not connect the grey.
 
2 valves. the CH works ok when i disconnect the SL from the water!
so it sounds like it's not gravity and is an Splan with a high limit/themal cutout as its unvented. So when HW is turned on, on the programmer the common on the cylinder thermostat should become live, cylinder thermostat is below the water temp then normally closed on cylinder thermostat should be live, normally closed should then go through the the thermal cut out and power up the brown of the valve, valve should then motor round and close the micro switch between grey (permanent live) and orange switch live. So if the valve is staying open and closing the micro switch then the body of the valve could be stuck but the plumber should pick this up when replacing the head or the brown is picking a feed up from somewhere as it must be wired wrong as the heads been replaced a few times it sort of rules out it being a dodgy head.
 
With the juice of and the orange and greys of valves removed is the switch closed. If it's open and there's a live on the orange could there be link passing a feed to valve at junction box, maybe the boiler pump arrangements have been changed. Ie over run and boiler is feeding outgoing side of micro switch. Just a thought could be Pish. Not the brightest when it comes to various boiler controls.
 
So, if it's a 2 port valve then it looks like the feed from the tank stat (S/L) goes to the brown, and orange to the boiler. You do not connect the grey.

Is that a fudge or should the head be swapped to the SZ 2351?

The home owner knows her house was built by bodgit and scarper so its the latest of her issues swallowing her money...
 
Last edited by a moderator:
Is that a fudge or should the head be swapped to the SZ 2351?

The home owner knows her house was built by bodgit and scarper so its the latest of her money swallowing her money...

I think it's a fudge Murdoch, though it should work.
The actuator is for a gravity fed system but if you wire it as the drawing and ignore the CH side of things it should work ok.
SL to brown, orange to boiler. There's no need to worry about the grey, that just brings on the pump for the CH in a gravity system. You've got another 2 port valve for that.
 
So, if it's a 2 port valve then it looks like the feed from the tank stat (S/L) goes to the brown, and orange to the boiler. You do not connect the grey.


Definatly not. Orange becomes live from the permanent live of the grey which should come from pl from boilers pcb. But from murdoch op it hasnt been wired with a 5c to boiler L,N, PL, SL, cpc. So it may be an older boiler which may not specify sl fed off pl on pcb so may have grey linked to pl in wc. It does sound like a Dodgy head apart from you say "wetpants" has changed the valve twice. Are you sure you werent getting back feed off ch orange.? Maybe fresh look at it will serve you well next visit, not a nice job last call of day!
 
I've just googled the valve and Andyb looks like he has it spot on. The valves not a conventional valve where grey is permanent live. Brown of the valve connects to normally closed of the cylinder thermostat and orange switched live to boiler/pump. The orange of this valve will also be commoned with the orange of the other valve. As this valve is usually for Gravity HW and pumped central heating I'm not sure if having the oranges from both valves together will affect by back feeding the valve if it does then it would be easier to replace the sunvic with a standard Honeywell two port.
 
Definatly not. Orange becomes live from the permanent live of the grey which should come from pl from boilers pcb. But from murdoch op it hasnt been wired with a 5c to boiler L,N, PL, SL, cpc. So it may be an older boiler which may not specify sl fed off pl on pcb so may have grey linked to pl in wc. It does sound like a Dodgy head apart from you say "wetpants" has changed the valve twice. Are you sure you werent getting back feed off ch orange.? Maybe fresh look at it will serve you well next visit, not a nice job last call of day!

It doesn't have a permanent live, it's the wrong valve.
You are correct in what you say if it was the correct valve, but there is no grey/orange S/l P/L for that valve.
Look at the drawing Murdoch posted in picture 3.

If you look you will see that when you put the switch live to brown the orange becomes live to feed the boiler. Like I said it's for a gravity system.
 
Well that's a bit of an interesting one!
Those valves are a bot of a pita sometimes, I've encountered them before and nearly lost the plot trying to work them out. Assuming it's the one I tikka it is!

I've had a bit much cider to be any help now, but I'll have a proper look at it tomorrow and consult my notes on boilers.
 

Reply to Ok, I admit it, I'm stumped...... in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
928
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
New build houses, full system boilers with the big cylinders with seperate thermal cut out and temperature probe which come with a pre fitted link...
Replies
5
Views
2K
Deleted member 26818
D
Story is i got called to finish off the heating on a new build as the electrician doing the work was too busy to get back in time. There were...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock