- Reaction score
- 20
Hi Guys,
I came across an old MEM board a couple days back with 3871 breakers and 5419 main switch. It was metal board with no earthing and relying on the trunking as mains of earthing (no main bonding). As well as this no RCD protecting to sockets.
Obs a fail. Would you code 1 or 2 this?
Also when recommending best course of action for remedials. Would you either a. Recommend a full board upgrade, or b. recommend main earthing added and a second small board to divert cables for sockets through a RCBO?
Ka value of the 3871's are 9ka so okay for continued use
thanks
I came across an old MEM board a couple days back with 3871 breakers and 5419 main switch. It was metal board with no earthing and relying on the trunking as mains of earthing (no main bonding). As well as this no RCD protecting to sockets.
Obs a fail. Would you code 1 or 2 this?
Also when recommending best course of action for remedials. Would you either a. Recommend a full board upgrade, or b. recommend main earthing added and a second small board to divert cables for sockets through a RCBO?
Ka value of the 3871's are 9ka so okay for continued use
thanks