Posting a message to the forum will remove the above advertisement

Discuss Outdoor socket flush with the ground in the garden in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. n180
    Offline

    n180 Active EF Member

    Is there a problem with installing an outdoor IP65 socket flush with the ground, fed via SWA cable?

    Are there any regs or issues I should be aware of besides the usual when installing outdoor socket on a wall? Of course, I have to make sure it's in a location where it may not easily be stepped on, or someone to trip over it.

    Also, if it is to be flush with ground, should it be flush with a concrete base around it or wood, or in some other enclosure?
     
  2. Baker1988
    Offline

    Baker1988 Electrician's Arms

    Location:
    Kingston Upon Hull
    If you put it flush with the ground woukd you still be able to plug stuff into it? Also ip 65 is protected from low pressure jets and if it is flush with the floor it might get slightly immersed in water (no fully) if it rains hard enough or drains back up which it is not rated for. I personally would not put it flush with the ground just raise it up a bit
     
    • Like Like x 2
  3. ImpededLoop
    Offline

    ImpededLoop Electrician's Arms

    Location:
    West Sussex
    The manufacturers instructions are likely to prohibit it. Also they normally require the accessory to be mounted vertically, not laid on its back.
     
  4. n180
    Offline

    n180 Active EF Member

  5. n180
    Offline

    n180 Active EF Member

    thanks for the info guys, just saw your responses after my alst post.

    Yes the immersion in water is a good point. And if the manufacturers instructions really prohibit then, I'll probably leav it.

    I take it this is not a common thing to do then?
     
  6. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    Just get a nice solid post put in (pref concrete), then fix your socket to it. The only electrical thing you want in the ground is a suitable cable.
     
    • Agree Agree x 2
  7. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    what i did when asked to fit one for a water feature was to hammer a couple of 4 ft lengths of unistrut into the ground, with a couple of cross bars sized to the double socket. then fed with SWA. socket attached to the strut with zededees and 6mm bolts.
     
    • Like Like x 2
    • Agree Agree x 1
  8. n180
    Offline

    n180 Active EF Member

    Thanks all, thats just the sort of info I needed. I'll get something solid into the ground to act as a frame to stick socket onto vertically.
     
  9. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    I would just make sure its well clean of the ground or mr and misses ant with all their kids will move in proto!
     
    • Like Like x 1
    • Agree Agree x 1
  10. tomspark93
    Offline

    tomspark93 Electrician's Arms

    Just sink it in to the outside wall...
    :rolleyes::D
     
    • Funny Funny x 2
  11. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    what a bodger. and why has he taken the cpc to the plastic back box instead of the socket.
     
    • Like Like x 1
  12. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    • Like Like x 1
  13. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Looks like a good solution however it does not seem ip66 with plug top inserted.
     
    • Agree Agree x 2
  14. LankyWill
    Offline

    LankyWill Electrician's Arms

    Location:
    Northants
    I use @telectrix@telectrix method aswell, it's the best method i think. In fact I think I stole it from him in another thread. Done one 6 months ago and no sign of rust, looks minimal aswell.
     
  15. Gazthesparky
    Offline

    Gazthesparky Electrician's Arms

    Location:
    Glasgow
    I haven't installed one myself but have used a few. There are special power pod things that are installed in the ground and then you wind them up when u want to use them. The ones I've used have 63a ceeform plugs fitted depends on your use really

    http://popuppower.co.uk/

    IMG_7004.PNG
     
    • Like Like x 1
Loading...
Similar Threads - Outdoor socket flush Forum Date
Checking other circuits after fitting outdoor socket? Electrical Wiring, Theories and Regulations Jun 28, 2017
Domestic 2 FCU in Series for Outdoor Socket DIY Electrical Forum Jun 4, 2017
Outdoor wiring question Electrical Wiring, Theories and Regulations Jul 5, 2017
Outdoor kitchen earthing Electrical Wiring, Theories and Regulations Jun 29, 2017
IP ratings of outdoor light fittings Lighting Forum Jun 25, 2017
Outdoor junction box for armoured cable Electrical Wiring, Theories and Regulations Jun 20, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job