Discuss Outside light - tripping RCD in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. hightower
    Online

    hightower Trainee Electrician's Arms

    Location:
    Durham
    Went to a job last week, replace an outside light with another customer bought one. Straight swap, few extra holes in the wall for new mounting, job done. Photocell model.

    Left the job with a working light. Now, I fitted this in the p***ing down rain, which in itself was a tad silly of me but I wanted this job out the way. I chalked it off as something damp inside and said I'd be back round to look in a few days when it dried up - not a problem as it has a switch so can be isolated leaving the rest of the electrics on and working.

    When I went back it hadn't rained since fitting, so should have been nice and dry in there by now. I checked and there was no wires trapped or anything. I'd asked if they'd tried it since and "no", so flicked it on and it works. Left the job, 10 minutes later a message to say it's tripping again.

    So the symptoms are the light works fine for a little while, but then starts tripping. Once it starts tripping it continues tripping until seemingly left a while.

    Probably a simple one as "dodgy fitting" but wanted to double check on here if anyone had any more thoughts? He's asked me to stick his old one back up, which I'll be doing this weekend at some point, but wanted a second opinion....
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    test the fitting as in pat.
     
    • Like Like x 2
  3. hightower
    Online

    hightower Trainee Electrician's Arms

    Location:
    Durham
    It'll likely pass though due to it not tripping for the first 10 minutes?
     
  4. DPG
    Offline

    DPG Electrician's Arms

    Location:
    S Yorkshire
    Not necessarily - the test will stress the insulation more, ie. 500VDC between neutral and earth.
    Daz
     
    • Like Like x 1
  5. Rob
    Offline

    Rob Trusted Advisor

    Location:
    North west
    Could always be something a miss in the photocell electronics.

    IR those an you'll likely break them.
     
    • Like Like x 1
  6. Richard Burns
    Offline

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    The light itself is unlikely to have any connection to earth in the circuitry so unless something is expanding whilst on and the circuit/lamp is then touching the body of the fitting I cannot see how the RCD would trip from the light fitting alone.
    Where did those extra holes for mounting the fitting go? perhaps near the supply?

    Also if the light had been changed before and there is a nice terminal block in insulation tape just inside the wall that got wet during fitting this may be a cause.
    On site investigation is the only way, though it would be interesting to see if it still trips with the old light!
     
    • Like Like x 1
  7. hightower
    Online

    hightower Trainee Electrician's Arms

    Location:
    Durham
    The cable is straight through so no chance of contact. Just finding it strange with it being a delayed trip rather than the second it's turned on
     
    • Like Like x 1
  8. Wilko
    Offline

    Wilko Gorillas are Great Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Any chance it's them turning something else on that's under that RCD?
     
    • Like Like x 1
  9. hightower
    Online

    hightower Trainee Electrician's Arms

    Location:
    Durham
    One rcd for install. Definitely not anything else as the light trips as soon as turned on (after the initial delay) - it's that delay turned instant symptom that's making me think electronics of the photocell?
     
  10. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    There could be a N-E fault somewhere else on the installation, sometimes the tripping can be completely unrelated to the apparent cause. Test the whole lot.
     
    • Like Like x 1
  11. AyresomeBoro
    Offline

    AyresomeBoro EF Member

    Location:
    Middlesbrough
    Another thought if all else tests out fine - Faulty RCD?
     
  12. sparksburnout
    Offline

    sparksburnout Electrician's Arms

    Location:
    Notts
    No point looking for complicated solutions, it would be very co-incidental if it was something other than the light (assuming it actually was working OK before!). Just stick the old one back and see how it goes.
     
    • Like Like x 3
  13. hightower
    Online

    hightower Trainee Electrician's Arms

    Location:
    Durham
    Thanks for replies everyone. Old one now back up and no issues, so had to be a faulty light
     
    • Like Like x 1
  14. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    I'd still of IR tested the install....would take 5 minutes to do a global. As it is you've made an assumption that may be correct but it's still an assumption.
     
  15. hightower
    Online

    hightower Trainee Electrician's Arms

    Location:
    Durham
    I didn't explicitly say I didn't test the install. I did IR test it and returned fine. Also clamp tested to see but that returned nothing interesting
     
    • Like Like x 1
  16. sparksburnout
    Offline

    sparksburnout Electrician's Arms

    Location:
    Notts
    How do you mean 5 minutes to do a global? Usually takes about 20 mins for the occupier to run round and unplug everything. Then you have to spend another 10+ mins working out whats still connected......problems pretty obvious here why complicate it??
     
  17. westward10
    Offline

    westward10 If I was in your DNA then you wouldn't be so ugly. Electrician's Arms

    Location:
    Northamptonshire
    Nah leave it all plugged in, IR to earth job done. Does not more harm than a PAT, if you get problems then unplug.
     
    • Like Like x 1
  18. sparksburnout
    Offline

    sparksburnout Electrician's Arms

    Location:
    Notts
    Yeah right on.
     
  19. sparksburnout
    Offline

    sparksburnout Electrician's Arms

    Location:
    Notts
    Nice one, don't make a drama out of it. Problems obvious, no need to conduct an inquest, times money! Tricky concept for some folks.....
     
    • Like Like x 1
  20. Des 56
    Offline

    Des 56 Trusted Advisor

    Location:
    Gliese 581C
    Yet another who deviates from the ABC of testing to improve and speed up fault finding in Domestic installs :thumbsup:
    After all,it's the fault that needs to be located and that can be installation or user cause,two birds with one stone and all that
     
    • Like Like x 1
Loading...
Similar Threads - Outside light tripping Forum Date
Outside lighting in a garden run in swa Electrical Forum Jun 12, 2017
Outside lighting for decking. Electrical Course Trainees Only May 18, 2017
Shower/outside light strange Electrical Course Trainees Only May 1, 2017
Large housing outside socket Electrical Forum Jun 9, 2017
Conservatory Light FCU Switch Change of Location Electrical Forum Yesterday at 11:05 PM
Installing Smart Light Switch Electrical Forum Yesterday at 5:18 PM
Emergency lighting - Borrowed Light Lighting Forum Tuesday at 2:27 PM
Dangerous lighting shades Commercial Electrical Talk Tuesday at 10:32 AM
Adding a light to a circuit with no earth Electrical Wiring, Theories and Regulations Tuesday at 9:59 AM
Astro plaster in down lights.. New Member Introductions Sunday at 10:11 PM

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job