Discuss oven/ hob diversity in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
0
Hi.
I am installing a new Hob and oven
the hob is induction 7.2kw
the double oven is 6.8kw and is to be hard wired

At the moment there is a 6mm 32amp supply for the hob
and a dedicated oven circuit on 2.5mm and 16 amp breaker

I have worked the oven with diversity to be just under 16amps.
I spoke to Neff who said it should be installed on a dedicated 20amp circuit.
without diversity it draws 29amps, could this cause a problem?
 
jujst change the 16A breaker for a 20A (assuming the 2.5mm cable's installation method allows for >20A and Zs complies for a 20A.
 
Hi. Thanks for your reply. That was my thinking. My main concern is that without diversity it draws over 29amps and if both were in use could this cause the circuit to trip? I have seen other ovens with lower power that say they require a 32amp circuit. Just thinking of the Christmas Day scenario when both are more likely to be used together. Thanks
 
yes, but with oven element/s on, the grill element would be off.an d if the manu. states a 20A circuit, then a 20A circuit is enough.
 
Last edited:

Reply to oven/ hob diversity in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
632
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
950
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
992

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock