On 'Pattesters' website they advise-

When testing modern IT equipment it is not normal to performed a leakage or touch current test; these tests are usually used on older equipment in place of the 500 Volt insulation test.

However in my copy of the IEE they say that touch current test should be used.

So if you are not using a leakage or touch current, I presume the only tests they are saying used on it are visual inspection & earth continuity test.
 
Correct!! The reason being; modern PC's momentarely start up when you apply power, then shut down automatically after about 10 seconds. When PAT testing the applied test duration is around 5 seconds. When 2 short bursts of power is applied to modern PC's
there is a potential of them "crashing".
 

Reply to P.A.T Testing I.T. Equipment in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock