H

Hottub

hi guys I have had an electrician come and put some wiring in ready for a hot tub delivery.

I passed on a electrical document sent to me by the hot tub company which had 6mm on it.

He has run a armoured 2.5mm 3 core cable from the main board and a dedicated 32amp mcb to an external rotary switch ( about 3 metres away ) also 32amp. From the switch he has run the same 2.5m 3 core around to where the hot tub will be ready to be connected ( no more than 4m away ).

He says its more than enough but as I've seen 6mm on the wiring diagram I'm worried.

So shall I stop worrying? Or demand he use 6mm? Or find a different sparky?

Thank you for your time.
 
it may well be that 2.5mm cable is adequate for the load, but the rating of the MCB should be below the design current, unless he's working on the principal that the tub is a fixed load and thus can dispense with overload protection. tin hat ready.
 
Seems very odd that he knows the rating of the hot tub then either totally miscalculates or is not competent.
 
all boils down to this:

1. what is the load current of the hot tub? get that from rating plate.
2. from the above, what size cable is required? from BS7671.
3. from the size of the cable, what rating should the OCPD be? Ib<In<Iz.

simpleesss.
 

Reply to Please put my mind at rest in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning. Needed some advice please. I am getting an AC condenser unit installed on an outer bedroom wall but only after some internal...
Replies
4
Views
930
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
381
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
993
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock