Discuss PME supply query (and bulk out the title) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
103
Hi all, I've been surveying 12 blocks of flats today with a view to doing full eicr's on the lateral mains and landlord lighting supplies. All the main services terminate at a Henly distribution board with no cut-out or main fuses. See pic, I've done very little on pme supplies and wonder if this is the norm? Appreciate your input. Bill
IMG_5677.JPG
 
to me billsays it pme system .but looking at the picture where are the fuse boards!

Hi Buzz, This is in an intake cupboard at the bottom of each block. Inside the grey Henly distribution board are fuses. Then a lateral main to each flat with another fuse/cutout beside each meter.
IMG_5671.JPG IMG_5681.JPG

(On the first photo in my original post ignore the meter thats just a builders supply thats been put in)
 
Is the cutout and mainfuse in the shaped compartment under the Henley dist board? You've the cover off of the flats supplies but the incomer goes to that shaped box.
 
Is the cutout and mainfuse in the shaped compartment under the Henley dist board? You've the cover off of the flats supplies but the incomer goes to that shaped box.

I had a look in there and it's just a spreader box. Didn't take a photo though.
The set up is the same for the whole estate, I've not come across it before.
 
Much as I love electric cupboards I haven't seen enough set ups to comment any more. There'll be plenty experience along in a moment, you'll have it sorted by pudding time. All the best
 
That isn't an uncommon set up there maybe a combined neutral/earth bar within to facilitate the TN-C-S.
 
That isn't an uncommon set up there maybe a combined neutral/earth bar within to facilitate the TN-C-S.

It's definitely a PME supply,
This cluster**** is the combined N&E connections and the line connections for the lower two banks of fuses.
IMG_5682.JPG
but it was the lack of single point of isolation/main fuses that struck me as odd.
 

Reply to PME supply query (and bulk out the title) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
527
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
154
Hi All, I have just completed an EICR on a new (2017) conversion and noticed the E7 looked unusual. Is this the norm now to connect E7 to the...
Replies
28
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock