Am thinking, there's a problem with the heated mirror.
Try disconnecting it, see what happens.
How could the mirror be causing this?
Discuss Problem with a timer fan on light circuit in the Lighting Forum area at ElectriciansForums.net
Am thinking, there's a problem with the heated mirror.
Try disconnecting it, see what happens.
now you're complicating the issue. my brain is conditioned for saturday afternoon. beer and kip.Could be on a humidistat, only come on if things steam up
If the voltage actually exists, as well as checking the switch, the remainder of the circuit (i.e. in other rooms) needs to be verified that its wired correctly. I had to fix a fault, where live had been connected into neutral and neutral vice versa.
bombay sapphire? sounds like an eastern belly dancer..
Who wired the mirror?How could the mirror be causing this?
Andy Capp?Who wired the mirror?
Errgh?Andy Capp?
Am thinking, there's a problem with the heated mirror.
Try disconnecting it, see what happens.
Well this morning I turned up with my meters and did an insulation test on the upstairs lighting circuit L N -E was 1.2Mohm which is just scraping through. Volts must be inducing through the cables insulation. Took the timer fan back and fitted a pullcord model and an Rcbo. Advised the customer its a rewire. Thanks guys for the input.I can't see how a problem elsewhere on the circuit is going to cause this, based on the information we have, the problem exists on the S/L therefore must be limited to the switch and the wiring after it.
L-Nwas 1.4 Mohm. Its a dorma bungalow with aflat roof. Only access to the wiring is all the ceilings down as its got eyeball spots and no idea where the Jbs are.It might be just a L/E, N/E fault somewhere and rewires not required.
Previous tennant, I presume.Who wired the mirror?
Well this morning I turned up with my meters and did an insulation test on the upstairs lighting circuit L N -E was 1.2Mohm which is just scraping through. Volts must be inducing through the cables insulation. Took the timer fan back and fitted a pullcord model and an Rcbo. Advised the customer its a rewire. Thanks guys for the input.
What would you have done?Err pull cord model and rcbo? Really
What would you have done?
Whats that?Post #38
Reply to Problem with a timer fan on light circuit in the Lighting Forum area at ElectriciansForums.net