Discuss Problem with a timer fan on light circuit in the Lighting Forum area at ElectriciansForums.net

Well this morning I turned up with my meters and did an insulation test on the upstairs lighting circuit L N -E was 1.2Mohm which is just scraping through. Volts must be inducing through the cables insulation. Took the timer fan back and fitted a pullcord model and an Rcbo. Advised the customer its a rewire. Thanks guys for the input.

Just scraping through?
Volts inducing through the insulation?
Advised a rewire?

Well that's a load of bovine excrement isn't it!
They don't need a rewire, they need an electrician.
 
You've ruled out the fan as being the problem as far as I can see, so now you need to track down where the this 9V is coming from.

What have you measured the 9V with reference to, earth or neutral?
if you have a suitable multimeter then try measuring it with that, I suspect it will give a higher voltage reading.

I think the simplest explanation for a voltage on the S/L when it shouldn't be is that the switch is not operating correctly, so I'd be inclined to test that first.
The 9 v was in every room upstairs when the switches were off.
 
looks like the mice in the house have stolen 221 volts from the upstairs lighting!
or their must have been a 9volts battery.
if thats the case I would have informed the person of the property .
 
Just read this thread,what a palava over a fan :)
The conclusion is a rewire is recommended because the fan is playing silly games ? :confused:

I have never tried that one :)
 
Whats the answer then Einstein?

Well it's certainly not that 'volts must be inducing through the insulation' As a result of a low insulation resistance.

No need to be Einstein to understand induction, it's taught in secondary schools after all!

I don't know the answer as I haven't visited the property and tested anything, but I'm pretty sure it wouldn't take very long to find the cause with a logical process and testing.
 

Reply to Problem with a timer fan on light circuit in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
962
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
384
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi All, Weird matter happening here and I hope you can help! My 3 Pahse EC Fan is connected to a sensor and a controller for the temperature...
Replies
2
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock