I'm at a bit of a loss as to how to proceed.

Had a Ze measured at 0.55 Ohms on a TNCS, contacted DNO who gave a asserted value of 0.52 Ohms. DNO came out and confirmed the result then checked over the earth path to the transformer, worked some magic and came back and measured at 0.44 ohms, they also de-rated the main fuse to 80 Amps from 100 Amps.

All good then? well no, tested today and it's back to 0.55 Ohms. So really wondering how to proceed with EIC.

1, record the result the DNO tested - 0.44 Ohms
2, record my measured result but make a note on the EIC that the DNO is aware of the high Ze.

This is not a test instrument issue as my, another independent spark and the DNO test instrument all tested to within 0.01 Ohms of each other.

This is my second visit, 300 mile round trip, to try to resolve an issue with the DNOs equipment, where do my responsibilities with this end?

The DNO have been contacted again, not sure of what they'll do but if they decide to de-rate the main fuse again we're going to have some serious load issues.

Any thoughts??
 
Last edited:
I'm at a bit of a loss as to how to proceed.

Had a Ze measured at 0.55 Ohms on a TNCS, contacted DNO who gave a asserted value of 0.52 Ohms. DNO came out and confirmed the result then checked over the earth path to the transformer, worked some magic and came back and measured at 0.44 ohms, they also de-rated the main fuse to 80 Amps from 100 Amps.

All good then? well no, tested today and it's back to 0.55 Ohms. regards to the So really wondering how to proceed with EIC.

1, record the result the DNO tested - 0.44 Ohms
2, record my measured result but make a note on the EIC that the DNO is aware of the high Ze.

This is not a test instrument issue as my, another independent spark and the DNO test instrument all tested to within 0.01 Ohms of each other.

This is my second visit, 300 mile round trip, to try to resolve an issue with the DNOs equipment, where do my responsibilities with this end?

The DNO have been contacted again, not sure of what they'll do but if they decide to de-rate the main fuse again we're going to have some serious load issues.

Any thoughts??
Do you mean this was a visit for an EICR ?
 
No, still trying to to issue an Electrical Installation Certificate. Ripped out old heating system, installed new. When tested found high Ze, informed DNO who have been out and resolved, gone back to re-do test only to find it is still high.
 
DNO normally stipulate 0.35ohms max for a ze
reading for TN-CS unless they stipulate higher which can be the case for rural areas.
You sure it's not TN-S?
 
No, still trying to to issue an Electrical Installation Certificate. Ripped out old heating system, installed new. When tested found high Ze, informed DNO who have been out and resolved, gone back to re-do test only to find it is still high.
Would have thought Ze should have been sorted at the onset of the works.
 
Would have thought Ze should have been sorted at the onset of the works.
Not possible with a two day job but it is something were looking to find a way to work with.
Just thinking out loud, but maybe paying a local spark to do Ze and sort with DNO if required.
 
DNO normally stipulate 0.35ohms max for a ze
reading for TN-CS unless they stipulate higher which can be the case for rural areas.
You sure it's not TN-S?
No, the Ze is ultimately what the DNO tell you it is. Not less than the 0.35 TNCS, 0.8 TNS, but they will, on request, give the exact figure for the area you are and this may well be higher than the above numbers.
 
What was the line/neutral reading.
What's you're thinking? Not sure of the relevance. To be perfectly honest if it's not required on the Cert then it's not something I've been trained to do or do do.

The system has been confirmed as TNCS by the DNO, as stated above.
 
What's you're thinking? Not sure of the relevance. To be perfectly honest if it's not required on the Cert then it's not something I've been trained to do or do do.

The system has been confirmed as TNCS by the DNO, as stated above.
Just a comparison I do when I get odd readings because if it is TN-C-S as they say you should get a similar reading, if not then something is amiss.
 
Just a comparison I do when I get odd readings because if it is TN-C-S as they say you should get a similar reading, if not then something is amiss.
I thought as much but as stated the DNO has confirmed it's TNCS.

Not sure my MFT is clever enough to do this, unless you attach the leads to the L - N -E as stipulated it comes up with an error and will not carry out the test. But I see the logic in what your suggesting.
 
Yeah I had a rural installation where the ze stipulated on tncs from DNO was 0.5 ohms.
Thankful it wasn't problematic as my zs values where still within tolerances.
It was all rcd protected via 30mA anyway.
 

Reply to Problematic Ze........ in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
828
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
953
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock