I'm at a bit of a loss as to how to proceed.
Had a Ze measured at 0.55 Ohms on a TNCS, contacted DNO who gave a asserted value of 0.52 Ohms. DNO came out and confirmed the result then checked over the earth path to the transformer, worked some magic and came back and measured at 0.44 ohms, they also de-rated the main fuse to 80 Amps from 100 Amps.
All good then? well no, tested today and it's back to 0.55 Ohms. So really wondering how to proceed with EIC.
1, record the result the DNO tested - 0.44 Ohms
2, record my measured result but make a note on the EIC that the DNO is aware of the high Ze.
This is not a test instrument issue as my, another independent spark and the DNO test instrument all tested to within 0.01 Ohms of each other.
This is my second visit, 300 mile round trip, to try to resolve an issue with the DNOs equipment, where do my responsibilities with this end?
The DNO have been contacted again, not sure of what they'll do but if they decide to de-rate the main fuse again we're going to have some serious load issues.
Any thoughts??
Had a Ze measured at 0.55 Ohms on a TNCS, contacted DNO who gave a asserted value of 0.52 Ohms. DNO came out and confirmed the result then checked over the earth path to the transformer, worked some magic and came back and measured at 0.44 ohms, they also de-rated the main fuse to 80 Amps from 100 Amps.
All good then? well no, tested today and it's back to 0.55 Ohms. So really wondering how to proceed with EIC.
1, record the result the DNO tested - 0.44 Ohms
2, record my measured result but make a note on the EIC that the DNO is aware of the high Ze.
This is not a test instrument issue as my, another independent spark and the DNO test instrument all tested to within 0.01 Ohms of each other.
This is my second visit, 300 mile round trip, to try to resolve an issue with the DNOs equipment, where do my responsibilities with this end?
The DNO have been contacted again, not sure of what they'll do but if they decide to de-rate the main fuse again we're going to have some serious load issues.
Any thoughts??