Anyone know a good way of sealing an an entry to a PVC conduit box to make it water tight?

What I'm wanting to do is use PVC conduit for an outside lighting installation. Where the lights are to go, my intention is to use a short length of flex from the light to a terminal in a T shaped conduix box. Now obviously, two of the three entries into that conduit box will be sealed by the entering conduit on either side but what about the downwards facing entry that is used for the flex? My thoughts were to use a compression gland, but they are threaded whereas the conduit boxes aren't. Also, on one of the conduit boxes, there will be a total of three lengths of flex exiting from the one conduit box entry so a compression gland would be totally out of the equasion for that one. Edit: I guess I just want to exhaust all the options before I resort to pumping it full of silicone haha.

Any ideas? I'm hoping my explanation is ok, if it isn't let me know and I'll try and elaborate.
 
Last edited:
With the T box solvent weld a very short length on conduit into the third spout then glue a female coupler onto the length of short conduit, this then gives you the threads to screw the stuffing gland into. Personal opinion use Wiska boxes and male adaptors that can screw directly into the boxes, then just screw the glands into the pre threaded knock outs
 
A female adaptor glued in using a extra short piece of pipe,then the stuffing gland screwed into the adaptor



I came third in that reply
bronze medal maybe :)
Hawk was a comendable 4th
 
Last edited:
Just be sure there’s an egress hole for damp. I’ve only worked on plastic stuff once, every box along with its joints were full of water.
 
I would have use an IP rated joint box. Any continuous conduit from that can be connected using male bushes and adaptors etc and the cable exit points can be stuffers.
 

Reply to PVC conduit question in the Australia area at ElectriciansForums.net

Similar Threads

Hi All. What is the best/preferred method when connecting 20mm conduit to a back box of a socket on an outside wall ? I am connecting a BG...
Replies
10
Views
3K
Looking for some advice; I am intending to mount two led downlights on pillars/brick walls either side of the garage door opening. I will drill...
Replies
4
Views
3K
Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
Replies
1
Views
4K
Just carried out an EICR on a flat that was wired in the 70s - with singles run in earthed conduit to each point and the trunking providing the...
Replies
29
Views
4K
My Current Setup (see image BEFORE.jpg): The wiring for my existing detached garage is shown (see image BEFORE.jpg). The house consumer unit...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock