Discuss Question regarding PFC on a sub board. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nazoom

Hi

I am trying to carry out Prospective fault Current (PFC) test on a sub board that that is RCD protected and is fed by a main board. My question is how to carry out this PFC (short circuit or earth fault) on the sub board? Do we put the Main switch off in the main board and place the line lead at the line point of RCD that is feeding the sub circuits and then the neutral lead goes on the neutral point of the RCD?

Many Thanks
 
Why? If your PFC/PSSC is in spec for the protective device at the origin, it has to be in spec further down the line assuming that your protective devices in sub board are the same kA ratings as the main board, ohms law. Just calculate it if you really want to record it.

Cheers.............Howard
 
So does that mean that the PSSC/PFC is the same for both the main board and the sub board? And is measured at the Main board?

Thanks.
 
So does that mean that the PSSC/PFC is the same for both the main board and the sub board? And is measured at the Main board?

Thanks.

As stated by Sirkit, its down to Ohms Law. The more ohms between you and the source of supply the less Amps you'll have....SIMPLES
 
the same as if you were doing it at the main board. switch the sub board main switch off with the feed from the main board still on. then measure from the incoming L to N, and L to E at the sub main.
 

Reply to Question regarding PFC on a sub board. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
654
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
615
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock