Up coming job....
fb currently in downstairs hall in a little cupboard- along with the head and meter.
job is a rewire anyways- but customer wants new fb moved into garage- on other side of wall to where it is at the minute. (Directly on other side of wall- litterally just popping through wall)

Run is <3meters but i will obviously have to drill a hole through the wall for my 25mm tails and 16mm earth

was planning on having a switched isolator where the old fb is- then tails into garage to new fb.

but as tails go through wall- guessing they need additional protection- do this by a upfront 100ma rcd?

cheers guys
 
but as tails go through wall- guessing they need additional protection- do this by a upfront 100ma rcd?

Passing through a wall is not something which requires additional protection by RCD. And even if it did, a 100mA RCD is not appropriate for providing additional protection - only fault protection.
 
just an isolator. no need for fused, although that is an option. maybe a wylex KMF with 80A fuse.
 
What's the point in moving if then if your having to have something there still??
Surely it's making it more costly and inconvenient??


Sent from my iPhone using Tapatalk
 
and i'd fit a short length of 25mm pvc conduit through the wall then feed tails through that.
 
as long as it's a straight piece, no bends. still be room for a mouse.
 
Passing through a wall is not something which requires additional protection by RCD. And even if it did, a 100mA RCD is not appropriate for providing additional protection - only fault protection.

You could say then Ristard that the OPs idea is fubar (fb) lol only messin no harm meant
 

Reply to Rcd for tails? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
388
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
538
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another...
Replies
75
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock