Changed a consumer unit everything fine all test came back hunky dory, but one RCD would not trip on the test button so swapped them around, same deal,I then got random trips from unassociated circuits IE kitchen ring plug in kettle and the opposite RCD would trip disconnect incoming earth RCD,s behave normally Ze .18 didn't clamp the earth to check any current flow did't think of it till on my way back, the only other thing I did after the tests was connect an outside light for the tenant to existing cable, so i am thinking a shared N any clues would be great
Dev
 
Please tell us you don't intend to leave cpcs disconnected:confused1:

And to go one further than this, not only should you not be disconnecting CPCs whilst the installation is energised, your IR tests should be carried out with all CPCs connected to the busbar and all bonding in place.
 
I think you have mis read my OP,

I don't think it's that the OP has been misread, than the fact you've explicitly stated you're going to be disconnecting CPCs with the assumption you will be re-energising (otherwise how would you be able to see that RCDs are behaving).

so my plan is to disconnect the earths one by one to get the RCD to behave and hopefully indentify the culprit
 
OK disconnect each circuit in turn,test RCD, if it behaves then the fault has been found

Or, and stick with me on this because it is a totally radical idea, you could plug in an IR tester and try and find the fault using the method every electrical book going would explain. You know, just a crazy thought?
 
An I-R test will almost certainly find this fault. My money would be a N-E fault, hence why only higher loads are causing issues.

As someone who's managed to get 'trusted advisor' status on here, this is a little worrying then you're just disconnecting things randomly.
 
Like I said done that and all test come back ok, but, and this is the bit that aint playing ball with every circuit without anything plugged in, cooker,shower immerse etc etc all disconnected and all bulbs out and in the switched on position doing a global IR I get a X reconnected everything I get random trips, dis main earth random goes away
 
An I-R test will almost certainly find this fault. My money would be a N-E fault, hence why only higher loads are causing issues.

As someone who's managed to get 'trusted advisor' status on here, this is a little worrying then you're just disconnecting things randomly.
Thats because you assume I am some sort of idiot
 
Disconnecting a cpc when there is a known fault to earth could raise the earthed parts of that circuit (or if you disconnect the main earth, then all exposed and extraneous parts) up to the line voltage which is not a safe thing to do.
I would recommend that if your IR tests are coming back OK and you cannot find the fault by dead testing that you disconnect a circuit entirely (i.e. at least line and neutral) to remove it from the installation. Then if you put a high powered load on another circuit and the RCD does not trip you have disconnected the faulty circuit and can start checking that one in detail.

In this way if a faulty circuit is still present the RCD will limit the risk.
 
Mud slinging aside, if you've done the dead tests in the correct order, you should of discovered the fault before the live tests. Once on a rewire, I discovered a neutral earth fault on a radial and decided to put it to one side for later, to get the other circuits on. Except I didn't and mixed it up with another radial and connected it up. Got to RCD test and wouldn't function, neither would RCD test button. Went back to basics, and discovered my mistake.

Happy hunting:)
 
Have you got an earth clamp meter?

I think you need to check the residual earth loss across the installation and I suspect you have a combination of a N-E fault and cumulative earth leakage from plugged in devices....
 

Reply to RCD issue, or is it? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
291
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock