Discuss Rcd not tripping in the UK Electrical Forum area at ElectriciansForums.net

D

Doctorsparks

I'm stumped, fitted new cu in one bed house today RCD would not trip using test button or on test. The only time it trips is when a load is put onto socket circuit, or the socket on the cooker isolator, no faults have been found during testing.
Its a TNC-S system ze of 0.16ohms IR of >999 on all circuits, zs good on all circuits.

i thought it may have been a defective RCD so I replaced it but no join? I have tested both RCD's on my board when I got home both worked!

Any ideas?
 
Are you certain the RCD was connected correctly...polarity?,load and mains sides correct?
Also test the RCD with the tester directly on the load terminals with nothing else connected.
 
Sounds like a neutral on the wrong bar.
 
I have occasionally tested an RCD at the L-N output, wondered why it would not trip and then given myself a good kicking for being so stupid. The test button always worked though.

If the RCD won't work with anything connected something simple is wrong, there were some RCDs that needed a few meters of cable atttached or they would not work, cannot remember the make though. Have you tried testing from the accessory? Not GN3 method but would give you more ideas. The test button should always work though.

Failing that contact the manufacturer.

Good luck.
 
if it worked when you tested it at home, then go back and re-fit (supply only) . check you have correct voltage l-n supply side, switch on and check load side then test. remember, it works by measuring imbalance.
 
Last edited by a moderator:
Might be worth double-checking the IR for evidence of N-E faults on any finals, not just the ones that cause tripping. A hard N-E short downstream of the RCD can prevent the test button working as well as failing tests with the MFT.
 
It's more of an annex. It's got cooker, one ring and two lighting circuits, it's just been renovated none of the wiring has been changed I'm just upgrading the board and earthing.

Thanks for for all the advice am there now going to disconnect everything re test and reconnect.

It's an excel?
 

Reply to Rcd not tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock