Discuss Rcd protecting new ring main in the UK Electrical Forum area at ElectriciansForums.net

D

davek

Hi all,
I have been to look at a job, in a unit who require extra socket in a office. It is one of those building that has been split into small units,
The supply is 3ph. Each unit is supplied from mains with separate meters and a 3pole isolation switch with bs88 fuse 63a.
the board is a merlin gerin isobar 4c. the breaker are c60hb. my thought where rcbo but I can only get a c rated 32a which using table b6 gives me 0.58 ohms the zs at supply to board is 0.18.any thought or suggestions.
thanks
Dave
 
Re: Rcd prottecting new ring main

Can you not spur off an existing socket, and install a rcd socket outlet?
 
Re: Rcd prottecting new ring main

I did not want to use existing as some of it looks quite old and shabby, don't think customer would go with the expense of 7 rcd sockets fitted the other thought I had was fit a small rcd c/u nect to the board and put in a 40a b type.
 
Re: Rcd prottecting new ring main

Your post never mentioned 7 new sockets mate,I'll think it over
 
Re: Rcd prottecting new ring main

first question is what's the design current of the new circuit. if it's office, then a lot of the load may be IT... low current but high integrity earthing.
 
Re: Rcd prottecting new ring main

Ok thanks sorry sometime you forget add these thing as was mainly thinking on the breaker there is about a 5 meter run to the office partion so cable length is a concern on r1+r2
 
Re: Rcd prottecting new ring main

as far as a I have been told just heater fan or some oil rad pc and printer just sort of wanted socket add all round for general use as far as I know
 
Re: Rcd prottecting new ring main

Ok thanks sorry sometime you forget add these thing as was mainly thinking on the breaker there is about a 5 meter run to the office partion so cable length is a concern on r1+r2

I'm pedantic Dave you mean R1+R2 surely, try ebay for a MG b type rcbo Ive just had a quick butchers and there seems plenty to chose from
 
so, say yout rfc circuit is 50m end-end. that will give you a R1+R2 of approx 0.25Ω. addthat to your 0.18Ω, gives a Zs for the circuit of 0.43Ω. well within the 0.58Ω you quoted for the RCBO.
 
Last edited:
hi pete
yes may have et one off net just ha a quick ring round must locals only ha c in some just sounds like it was something odd
 
Can you get 20amp type c or b? If it's a small office you could wire a couple of radials in 4mm which will give you plenty to play with
 
so, say yout rfc circuit is 50m end-end. that will give you a R1+R2 of approx 0.25Ω. addthat to your 0.18Ω, gives a Zs for the circuit of 0.0.43Ω. well within the 0.58Ω you quoted for the RCBO.

yes hope full, just didn't want be to near the limits, but may order a b type just found one on tlc cheaper than the c breaker I have so that may be the answer
 
The Schneider KQ range come in type B, simply buy one of these and remove the clip on attatchment and there you have a type B MCB that will fit this board.
 

Reply to Rcd protecting new ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
963
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
878
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock