Hi wondering if some1 can advise me on a job I have been doin I've run a 10mm swa 3core to a outer building office mostly buried into a consumer unit protected by a rcd . At the house end consumer is it best to terminate in rcd side of board? or general supply side ?... Because if I terminate in rcd side if a fault was to occur in outer building it would interfere with power in house or do I place a separate rcd next to house consumer ?
 
the SWA does not require RCD protection. RCD is best fitted at the outside building. the only time you need RCD at the front end is if there's T/E buried in walls in the house before joining to SWA.
 
Thanks no nothing buried at house end just exits board into plastic adaptable box then swa out to outer office which is 30m away
 
then feed from a non-RCD way in the house CU. fit RCD/s in office.
 
Why do you want to create a situation where you would not have any discrimination between the two RCD's?? Supply the outbuildings SWA cable from the unprotected side of the main consumer unit!!!
 

Reply to Rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
679
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
835

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock