When doing the rcd test on sockets. Do you repeat the test at every socket in the ring or just at the middle of the ring, and within what time does the rcd have to trip at x1 its tripping current 200ms or 300ms? Thanks
 
When doing the rcd test on sockets. Do you repeat the test at every socket in the ring or just at the middle of the ring, and within what time does the rcd have to trip at x1 its tripping current 200ms or 300ms? Thanks


doing the tests at roughly the middle socket is exceptable and the tripping times of rcds depends on the rating of that particular rcd ie 30mA IS 40ms
 
When doing the rcd test on sockets. Do you repeat the test at every socket in the ring or just at the middle of the ring, and within what time does the rcd have to trip at x1 its tripping current 200ms or 300ms? Thanks

If you do the tests at the DB, it can be a lot easier and faster.

For a BS61009/61008, the 1X maximum trip time is 300mS.

For the older BS4293, the 1X maximum trip time is 200mS.

Both should have a max of 40mS on 5X
 
When doing the rcd test on sockets. Do you repeat the test at every socket in the ring or just at the middle of the ring, /QUOTE]

You are testing the charecteristic of the Rcd,this should be done on the load side with all loads disconnected
As advised,it is best tested at the consumer unit
You dont have to Rcd test at the sockets themselves,anywhere on the ring
 
doing the tests at roughly the middle socket is exceptable and the tripping times of rcds depends on the rating of that particular rcd ie 30mA IS 40ms



It does'nt make any difference where in the circuit you do the test from, given the opperating speed of an RCD the closer to the rcd the easier it is to reset during the test cycle.
 
Yes but if the RCD is required work in real life the load will not be disconnected, so don't think that they are always going to react as your tester said they would.

I'm telling you the correct procedure for rcd testing as per IEE Guidance Note 3, not my opinion...
 
GN3 recommends to test between the the line conductor of the circuit and the cpc with the load disconnected.

This could be done at ANY socket and NOT the CU. You cannot have implemented safe isolation and test at the CU as the RCD test is a live test.
 
Last edited by a moderator:
GN3 recommends to test between the the line conductor of the circuit and the cpc with the load disconnected.

This could be done at ANY socket and NOT the CU. You cannot have implemented safe isolation and test at the CU as the RCD test is a live test.

As is Ze and PFC....
 
The RCD disconnection time test is not mandatory in the BRB, the functional test is.

This is because complying with the Electricity at Work Regulations cannot be met for applying all RCD tests.
 
the functional test will not determine nuisance tripping and only detects the mechanical functioning of the rcd
 
Last edited by a moderator:

Reply to Rcd test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
291
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
519
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
735
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
812
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
620

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock