    I've got a 3 phase DB with individual RCBO's supplying various equipment, Fire Alarm Controller/Water Heaters/Office Sockets/Office Lighting/Air Conditioning Controller.

    GN3 suggests "Any load or appliances should be disconnected prior to testing", would it be ok remove the supply at the RCBO for this and is it necessary to remove the load?
     
  2. to hide this advert.
  3. Richard Burns

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    Just take line and neutral out of the RCBO (work safely) or make sure the kit is switched off before testing.
     
  4. dazj90

    dazj90 EF Member

    Would removing the fuse from a spur be sufficient enough to remove the load as there are a couple of circuits that feed a spur then the device.
    Full arc flash gear will be worn under companies rules.
     
  5. dazj90

    dazj90 EF Member

    Also , is there a standard form to complete with just RCD quarterly test results, or would I just complete the RCD times section on the EICR form?
     
  6. Richard Burns

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    Yes removing the fuse would be sufficient, or just switching the spur off if it has a switch.

    I do not believe there is a standard form for quarterly RCD testing.
    I would either create your own form or modify say a minor works certificate to an RCD testing report.
    Something like this depending on what you need to report
     

    Attached Files:

    dazj90 and Vortigern like this.
  7. dazj90

    dazj90 EF Member

    Thank you for your help Rich.
     
Loading...
Similar Threads - RCD Testing Remove Forum Date
Problems testing RCDs/RCBOs Electrical Forum Dec 7, 2016
Testing RCD, The manufacturers response! Periodic Inspection Reporting & Certification May 25, 2016
2008 DB and RCD Electrical Wiring, Theories and Regulations Friday at 7:58 AM
Time delay RCDs and cables in walls Periodic Inspection Reporting & Certification Mar 19, 2017
RCD issue, or is it? Electrical Forum Mar 15, 2017
Hi, new guy here & some help needed with RCDs New Member Introductions Mar 13, 2017
Outbuilding on non RCD side of C/U? Electrical Forum Mar 12, 2017
no rcd circuit on 5x5 splitload board Electrical Forum Mar 7, 2017
lack of 30ma rcd protection Commercial Electrical Talk Mar 4, 2017
RCD needed With minor works? Electrical Forum Feb 25, 2017