Discuss RCD Tripping, Nothing in Sockets, no load... what now? in the Australia area at ElectriciansForums.net

T

Tidy

Hi Everybody,

We just moved into a detached house in last friday, only to find that the RCD keeps tripping for no reason :S I have had an electrician out who checked the RCD and said the box is fine.. and must be the sockets.

We unplugged every item in the house and tried to turn the socket switch back on (on the CU)... it trips the RCD, after 4 or 5 attempts it holds and we have power. (lights etc are not affected).

If we press the test button the RCD main switch does as it should.... and if we turn the socket switch OFF the main RCD will switch on immediately and hold. If we start to plug items back into the sockets sometimes it trips... sometimes it does not... there is no pattern.

I have pulled all the sockets away from the wall to make sure there are no trapped wires and for any interference with the back plates.. all ok, and still trips for no real reason.

The electrician (as above) has tested the CU with some little plugin things and said its fine and working as it should.

The worst time is the morning (between 8 - 10am), there are no washing machines on, no dryers, the combi boiler is off.. so essentially no load at all.

Other notes of interest is the previous owner who i have contacted (because of mail he needs to pick up) asked about the electrics... his words were

"its the shower, if i wanted to use the shower i had to make sure the washing machine, dryer and microwave was off). I had all the sockets tested and my electrican could not find anything wrong with the wiring.

Surely that would affect the shower switch... and not the sockets switch (the shower is not on the sockets - tested that lol).


I am sorry to pick everybodies brains, but i will go through when it has tripped and see if somebody is blatantly obvious?

1) Plug in extension cable with nothing in... Sockets RCD flicked as well as main RCD
2) Plug in hoover into kitchen socket.... main RCD off
3) Walking across the landing towards the shower... main RCD switch off
4) Jumping on the landing floorboards...no change (in case of rogue nail in floor boards lol)
5) Turning TV sockets on (which has an xbox, DVD player, 50" plasma, Wii), sockets rcd off, main switch off
6) 2 minutes into a shower, sockets off, shower off, main rcd off

This morning when i was just about to have a shower and had to reset the main switch, when i managed to finally get all switched to stick there was a buzzing noise coming from the CU - but it only happened when the shower was turned on (electric shower).

I am at a real loss at what to try next, with everything seeming to be checking out i seem to working (web designer) out of fear that my PC will shut down at any time with no warnings etc...

I am no expert but after many nights browsing the web and trying to diagnose the issue, would it be possible to think that it might be an earth problem for the house?

Thank you all again :)
 
Hi, It could be a fault on the cables which would show up with an insulation resistance test or it could be a neutral wire connected in the wrong place in the consumer unit. You need a sparks who is used to fault finding to test everything. You talk about having 2 RCDs - they should not be connected from one to another but both direct from the main switch. This way only part of the electrics will turn off not the whole lot. If you can email a photo of the C.U. with the cover off I might be able to help more. [email protected]
 
Hi,

Thank you for the reply. I think i may have my terminology all mixed up, i am just a mere designer lol

The RCD part is on the left with poorly labelled switches....

There is (from what i can read)

Shower
Cooker
Sockets
Sockets - Garage
 
I would test the shower wiring,get an electrician who has the correct test equiptment,its a traceable fault,it has been known before for spiders and such like to be across terminals on things and thats why tripping occurs occasionaly,could be a simple fix or might take longer,but a good electrician will trace it/test and put your mind at rest.what area do you live,perhaps a forum member may be able to assist.
 
Could the shower wiring affect the sockets though? I thought (probably incorrectly) that the whole point of an RCD is to only disable the offending circuit?

I am in the midlands... robin hood country lol
 
echo rob here. correct test gear is essential to trace this fault. there could be a connection lurking away out of site, or possible water ingress somewhere. post your location, one of us may be close to you.
 
Hi, do I take it that it's the same RCD unit that's constantly tripping?
If so, it might be an idea to swap with another of the RCD's that you have protecting the other circuits, just to see if there's a fault on the device itself.
I also notice that on your c.u schedule there's no mention of your boiler? It may be a long shot, but if it's supplied by this rogue circuit and you're problem is approximately the same time each morning - and this happens to co-incide with when your boiler fires up your heating - you may have a fault on the pump or internal PCB.
Either way, I'd suggest getting an experienced spark involved who's a confident fault-finder.
 
Hi Everybody,

Our electrician is coming back next week but if he can't find the fault i will contact those of you who have PM'd me (thank you)

When the electrician came out, he swapped one of the switches with another circuit in case it was faulty. He also said that after many times of tripping some switches become easier to break (ie, less resistance) which he said is not happening with ours.

We tested things with the boiler off, so could it have an affect?
 
if the fault is N-E as opposed to L-E, then an appliance that is switched off could be the problem unless the socket/FCU that supplies it is double pole. N-E faults sometimes give bizarre reactions from RCDs.
 
So with all appliances unplugged, it might be as simple as a socket that is not wired up correctly? (forgive me if i have completely mis-understood your post)
 
if a socket is incorrectly wired, the fault would generally only become apparent when a load was applied.
 
it's impossible to diagnose on the forum. generally if you have a L-E fault, it will not manifest itself with the breaker turned off. however, these faults are the pig's ear in how they appear. only with a thorough test can this be found if you have eliminated appliances by unplugging.
 
Thank you, I hope we can get to the bottom of it.

One thing that still worries me, is the buzzing we get from the CU when the shower is on? At our old house this never happened... the only noise from the shower was generally me singing...
 
could be that the shower is overloading it's breaker, but not enough to trip it. a breaker of . say 40A, will stand around 57A for up to an hour before tripping, but may buzz.
 
I mis-diagnosed a grey water pump coming on when the cu was energised. It was the rcd fizzing. The rcd tested fine on the normal tests. Strange thing was it only fizzed when it felt like it and the fizzing did not cause it to trip but it did trip randomly. Took a while (a good while!) to diagnose, all terminations were good, rcd seated correctly etc etc but by replacing what appeared through testing to be a perfectly good rcd, problem solved
 
It could be any number of things or a combination of any number of things including a faulty rcd.
The danger here is that in your desire to give your electrician as many clues as possible to what appears to be a simple problem you could get frustrated and careless and touch something you don't want to be touching. By removing socket fronts etc you could introduce another fault (trap a cable for instance) which makes the diagnosis even harder for your electrician.
Anybody who has pm'd you from here is showing a high level of confidence in being able to correct your problem so contacting them would be my next step if your existing electrician gets stumped.
 
Thank you mharries1, there is no way i would jump into trying anything myself. Changing sockets and basic stuff like that i dont mind having a fiddle, but somebody on the thread asked for a pic of the CU wiring... there is no way im taking the cover off just out of protection for myself.

I wanted to get an insight into what the problem may be, not to advise the electrician that is coming, but to possibly understand what he is trying and if he is stumped offer some of the comments on here as just "another brain" so to speak.

I do appreciate everybodies help, and fingers crossed all will be sorted this time next week. If not i will be back and phoning some of the kind people who have sent me some PM's.
 

Reply to RCD Tripping, Nothing in Sockets, no load... what now? in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
771
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
441
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
715

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock