Discuss RCD Tripping..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

dlt27

-
Reaction score
26
Can anybody help... Went to a job Friday where apparently RCD is coming out once every couple of nights. The rcd covers 4 circuits which are sockets, sockets, heating and outdoor shed. I have carried out a blanket test and I am getting a reading of about 20M This is with loads conncted apart from 2 neon extension leads which if connected brings it down to 0.39M.(still to high to cause tripping). I have also done a ramp test on rcd and it comes out at 23mA. Finally put clamp meter around tails serving rcd and with loads connected was still only getting 10.5mA of earth leakage. Thanks for any advice.
 
Can anybody help... Went to a job Friday where apparently RCD is coming out once every couple of nights. The rcd covers 4 circuits which are sockets, sockets, heating and outdoor shed. I have carried out a blanket test and I am getting a reading of about 20M This is with loads conncted apart from 2 neon extension leads which if connected brings it down to 0.39M.(still to high to cause tripping). I have also done a ramp test on rcd and it comes out at 23mA. Finally put clamp meter around tails serving rcd and with loads connected was still only getting 10.5mA of earth leakage. Thanks for any advice.

what kind of loads are connected
 
Washing machine, freezer, electric fence fed from shed, kettle, boiler. Even ran up heating but earth leakage still didn't go above 10.5mA. Did mention fitting rcbo's but if its an appliance breaking down this wouldn't help( just cause more expense).
 
From your testing the circuit wiring seems OK, therefore you are now heading for connected equipment with an intermittent fault, always a nightmare.
You probably need to do some investigation of the times and weather conditions when the RCD trips. If the trip is over night then it is only likely to be items that are running overnight.
Because some of the items are outside it could be water ingress, since you have 10mA already you only need another 13mA to trip it.
Could the electric fence be shorting when something pushes against the fence.
Freezers can be prone to tripping RCDs when old, less likely, but maybe you could run the freezer on an extension lead from another circuit for a few nights and see if the other circuit trips.
Did you run the ashing machine as these often break down to earth, but only when X item is activated, do they run the machine overnight?
 

Reply to RCD Tripping..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock