In the end, it was a L-E fault ... One of the lights had too much insulation around it causing the wiring insulation to become brittle and eventually short.

All is good now ...
 
In the end, it was a L-E fault ... One of the lights had too much insulation around it causing the wiring insulation to become brittle and eventually short.

All is good now ...

What about the N-E short you said you had found? Did the L-E short not trip the MCB?
 
We opened up the switch box and eventually the electrician determined that it was not the N-E short. The N-E fault was a false alarm probably triggered by the RCD (not sure about that) ?
The L-E fault was still resistive, low enough to trigger the RCD, but high enough not to draw too much current.
Goes to show that electricians and builders have different mindsets ... I guess the builder was over-keen to put insulation in the ceiling ... and just overdid it. The electrician on the other hand did anticipate this and created enough space around the lights.
In any case, I'll be switching to LEDs from now on ... less heat and power dissipation !
 
The N-E 'fault' is most likely the N-E loop of a TN-C-S installation. If you're not an electrician, with TN-C-S you have a line conductor and a neutral conductor coming in to the service head. The earth is then linked to the neutral conductor. TN-C-S stands for Terra Neutral Combined Separate as in earth/neutral combined (in the cable) and then separate (at the service head).

On the consumer side, if the installation is not fully isolated you will get a continuity reading between earth and neutral which is why you should fully isolate circuits for this kind of fault finding.
 
Thanks SparkyChick ... I drew the line when I have to open up my consumer unit.
Maybe later in the year (can't believe June is coming to an end !) I will enroll in a course and get qualified as an electrician to better protect my house !

btw, I had the electrician test my RCD again to make sure it is all working and it is.
 
agreed ... but it is a start. I am already competent in most things electrical/electronic ... but do not know much about a household (or industrial) installation as well as all the tests that are typically performed. Saw my electrician's Kewtech KT65DL and I was already drooling ... =)
 
The N-E 'fault' is most likely the N-E loop of a TN-C-S installation. If you're not an electrician, with TN-C-S you have a line conductor and a neutral conductor coming in to the service head. The earth is then linked to the neutral conductor. TN-C-S stands for Terra Neutral Combined Separate as in earth/neutral combined (in the cable) and then separate (at the service head).

On the consumer side, if the installation is not fully isolated you will get a continuity reading between earth and neutral which is why you should fully isolate circuits for this kind of fault finding.
Will happen on TN-S also as neutral and earth connected at the star point of the transformer :)
 
Thanks SparkyChick ... I drew the line when I have to open up my consumer unit.
Maybe later in the year (can't believe June is coming to an end !) I will enroll in a course ,perhaps in November,and by Christmas I'll officially be qualified as an electrician to better protect my house !

btw, I had the electrician test my RCD again to make sure it is all working and it is.
Corrected that for you to be more realistic with current training requirements.
 

Reply to RCD trips a few minutes after lights turned on in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
Kitchen led lights have all of a sudden dimmed by about 30% no dimmer in the system. There are 2 switches for this set of lights. Regardless of...
Replies
2
Views
815
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock