Currently reading:
RCD Trips when we get heavy rain?

Discuss RCD Trips when we get heavy rain? in the UK Electrical Forum area at ElectriciansForums.net

A

AshFR

Hi all. Got a bit of a problem. When we get heavy rain like we did today, the RCD trips. So i push it back on and sometimes it will stay there for months or it sometimes again instantly. Any idea what the problem is? I do have 2 outside lights and a PIR sensor on them. Im thinking the problem lyes there :) but could do with a bit of advice to testing it. It will come in handy aswell as i need a fault finding job for my college work :D Thanks all.
 
I would isolate the suspect fitting at the point of supply and test the circuit and fitting together. Might be worth just running a 250v test, the passive might not enjoy the higher voltage tests.
 
Hi all. Got a bit of a problem. When we get heavy rain like we did today, the RCD trips. So i push it back on and sometimes it will stay there for months or it sometimes again instantly. Any idea what the problem is? I do have 2 outside lights and a PIR sensor on them. Im thinking the problem lyes there :) but could do with a bit of advice to testing it. It will come in handy aswell as i need a fault finding job for my college work :D Thanks all.

The devil is in the detail, if your going to fault find start with the bottom and work up.
What are the supply arrangements ? TT TNS or TNCS ? this may then lead us on to where the RCD (s) may be in the installation, is it an up front RCD as a main switch or a split load board ? sounds like you have a spur off a RCD protected radial/ring ?..Not good,get back to us but I suspect if it is fed from another circuit, pulling the L/N out will cure it
J
 
I'd be tempted to isolate and have a quick look at the outside lights, their drains probably can't keep up with heavy rain.
 
The devil is in the detail, if your going to fault find start with the bottom and work up.
What are the supply arrangements ? TT TNS or TNCS ? this may then lead us on to where the RCD (s) may be in the installation, is it an up front RCD as a main switch or a split load board ? sounds like you have a spur off a RCD protected radial/ring ?..Not good,get back to us but I suspect if it is fed from another circuit, pulling the L/N out will cure it
J

It is a TNCS system :) The RCD is a main switch in the C/U.
 
Can I also remind you to carry out a full isolation procedure with lock off fella, PIR's and Photocells are especially risky, I hope you have your testers, if you have a RCD as a MS it will be DP so your good to go,but breakers are SP so beware of N faults, test test test !
J
 
Can I also remind you to carry out a full isolation procedure with lock off fella, PIR's and Photocells are especially risky, I hope you have your testers, if you have a RCD as a MS it will be DP so your good to go,but breakers are SP so beware of N faults, test test test !
J

Yes buddy. Always do :d Why are PIRs risky then? Yeah its definatly as a MS. :D

IF the spur is a DP isolator as opposed to a FCU it will clear the fault, if not you will need to whip the N out after the safe isolation is carried out
J

Well theres just a cable coming from a perm live to a normal switch then out to the lights/PIR.
 
Well some naughty boys..Use a 3 core as a L/N/ E as sw L this is common, especially on PCells,I had it this week on some pyro,naughty very naughty boys, assume nothing you will live longer lol, get a GS 38 tester and use it mate ALWAYS
 
As others have said make sure its dead before you start your tests,someone once said "Is it dead and I,m alive or was it live and I am dead?"get it wrong and thats one question you will never know the answer to!I owe all of my experience to the fact that I take safety seriously thereby living long enough to get experience.
 

Reply to RCD Trips when we get heavy rain? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top