I am helping a friend with extending the ring main and adding some lights etc... in his new bedroom. I have put in a few new sockets & some two way lighting etc... I have isolated the circuits by turning off the appropriate MCB's at the CU which is split and both sides are protected by RCD's I cant kill the lot as the Fire Alarm activates and my mate doesn't know how to deactivate the alarm completely. This isn't a problem until I cut a cable and even though the circuit is off (MCB off) the RCD trips. I am guessing that as I have only killed line, the neutral and earth are still connected to the CU when I cut through it is causing an imbalance but I thought there needed to be a current flowing for the RCD to operate and to detect the imbalance. Surely neutral & earth are both at 0 if I have broke the circuit at the line by switching off the MCB? I don't understand how it all works, any help would be greatly appreciated.

Thanks in advance.
 
Current will take any path available.
So the current on the circuits you have not de-energized is flowing through the RCD along the line conductor, then along the neutral conductor to the neutral bar, then back through the RCD.
By cutting through both the neutral and the earth conductor at the same time, you have created another path for the current to flow.
Some of the current when it reaches the neutral bar, will then flow along the neutral conductor you are cutting, along the earth conductor to the earth bar and then to the cut out where it will rejoin the rest of the current that is in the neutral conductor.
As the earth conductor does not pass through the RCD, the RCD will not register that current, as such it registers that X amount of current flowed up the line conductor, but only X minus the amount that flowed down the earth conductor returned along the neutral. As those two values are diferent, the RCD will operate.
 
Thats a great reply, thanks! I was half way there in my head but now its much clearer. Brilliant! Thanks. Is this the same reason that when I test for voltage on a circuit that I have turned off at the MCB I get the phase indication light on my tester but no voltage?
 

Reply to RCD's tripping with no current? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
566
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
715
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
717

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock